I am assuming that you are on the 2009 IBC. The code takes precedence over the 
standard. The sprinklers are required.

102.4 Referenced codes and standards. The codes and standards
referenced in this code shall be considered part of the
requirements of this code to the prescribed extent of each such
reference. Where differences occur between provisions of this
code and referenced codes and standards, the provisions of this
code shall apply.

Peter Schwab
VP of Purchasing and Engineering technologies

Wayne Automatic Fire Sprinklers Inc.
222 Capitol Court
Ocoee, Fl 34761

Mobile: (407) 468-8248
Direct: (407) 877-5570
Fax: (407) 656-8026

www.waynefire.com



We're hiring great people at all of our locations!  Please check out our 
website for the details! 



-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Richard Mote
Sent: Thursday, November 19, 2015 3:28 PM
To: [email protected]
Subject: Covered patios and decks in 13R

We have a project, a four unit apartment / condo which consists of two double 
stacked units. On one side of each 1st floor units is a little 2'-8" deep  
balcony that sticks out between the 1st and 2nd floors creating a really small 
covered patio on the first floor. The builder doesn't want to install 
sprinklers under these on the 1st floor. 13R doesn't address decks or balconies 
that I can find. But IBC 2009 (current in effect in PA) 903.3.1.2.1 says I have 
to provide sprinkler protection for exterior balconies, decks and ground floor 
patios, and doesn't give a minimum size. Should I just tell the builder he has 
to have them? Or is there a way out of it that I'm not seeing (he claims he has 
never had to do it before). The current addition of NFPA 13 in effect in PA is 
2007.

Richard L. Mote CET
Design Manager
Rowe Sprinkler Systems, Inc.
P 570-837-7647 or 877-324-ROWE
F 570-837-6335
[email protected]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org