What Pete said.   Slap a dry sidewall under those decks and be done with it.   
Sell sprinklers!  Sell, sell, sell ...

SL





-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Pete Schwab
Sent: Thursday, November 19, 2015 12:41 PM
To: [email protected]
Subject: RE: Covered patios and decks in 13R

I am assuming that you are on the 2009 IBC. The code takes precedence over the 
standard. The sprinklers are required.

102.4 Referenced codes and standards. The codes and standards referenced in 
this code shall be considered part of the requirements of this code to the 
prescribed extent of each such reference. Where differences occur between 
provisions of this code and referenced codes and standards, the provisions of 
this code shall apply.

Peter Schwab
VP of Purchasing and Engineering technologies

Wayne Automatic Fire Sprinklers Inc.
222 Capitol Court
Ocoee, Fl 34761

Mobile: (407) 468-8248
Direct: (407) 877-5570
Fax: (407) 656-8026

www.waynefire.com



We're hiring great people at all of our locations!  Please check out our 
website for the details! 



-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Richard Mote
Sent: Thursday, November 19, 2015 3:28 PM
To: [email protected]
Subject: Covered patios and decks in 13R

We have a project, a four unit apartment / condo which consists of two double 
stacked units. On one side of each 1st floor units is a little 2'-8" deep  
balcony that sticks out between the 1st and 2nd floors creating a really small 
covered patio on the first floor. The builder doesn't want to install 
sprinklers under these on the 1st floor. 13R doesn't address decks or balconies 
that I can find. But IBC 2009 (current in effect in PA) 903.3.1.2.1 says I have 
to provide sprinkler protection for exterior balconies, decks and ground floor 
patios, and doesn't give a minimum size. Should I just tell the builder he has 
to have them? Or is there a way out of it that I'm not seeing (he claims he has 
never had to do it before). The current addition of NFPA 13 in effect in PA is 
2007.

Richard L. Mote CET
Design Manager
Rowe Sprinkler Systems, Inc.
P 570-837-7647 or 877-324-ROWE
F 570-837-6335
[email protected]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to