What does it say in your words Ron, for those like me whom are too sick
and/or tired to look it up?
On Dec 25, 2015 7:26 PM, "rongreenman ." <[email protected]> wrote:

> Look in 13/2013 8.15.5.1. Specifically says to use a sidewall in an
> elevator pit. Commentary in the Handbook (p. 397) discusses the
> justification(s).
>
> On Fri, Dec 25, 2015 at 3:30 PM, Rahe Loftin - 7PMC <[email protected]>
> wrote:
>
> > Charles,
> > True if the elevator car is within 12 inches of the head but, of course,
> > not when it is any other position. Furthermore, what about the listing of
> > the sidewall head for a flat, horizontal, smooth ceiling?  This certainly
> > does not describe the bottom of an elevator car.
> >
> >
> >
> > *Success Through Code Compliance*
> >
> > *Rahe Loftin, PE  *
> > *Regional Fire Protection Engineer*
> > *General Services Administration*
> > *Region 7 - TX, OK, NM, AR, LA*
> > *Facilities Management & Support 7PMC*
> > *c - 817-371-3102*
> > *o - 817-978-7299*
> >
> > On Fri, Dec 25, 2015 at 7:37 AM, Charles Thurston <[email protected]>
> > wrote:
> >
> > > Hello Rahe,
> > >
> > > Works good when the car is at the bottom of the shaft.
> > >
> > > Friday, December 25, 2015, 7:11:21 AM, you wrote:
> > >
> > > > Sidewall heads without a wall is one thing, but what about sidewalls
> at
> > > the
> > > > bottom of elevator shafts that have a wall but no ceiling?
> > >
> > >
> > >
> > > > *Success Through Code Compliance*
> > >
> > > > *Rahe Loftin, PE  *
> > > > *Regional Fire Protection Engineer*
> > > > *General Services Administration*
> > > > *Region 7 - TX, OK, NM, AR, LA*
> > > > *Facilities Management & Support 7PMC*
> > > > *c - 817-371-3102*
> > > > *o - 817-978-7299*
> > >
> > > > On Wed, Dec 23, 2015 at 7:42 PM, Brad Casterline <
> > [email protected]
> > > >
> > > > wrote:
> > >
> > > >> A few more things Sean then I'll be able to sleep-
> > > >> 1) you're welcome
> > > >> 2) you have put a lot of good thought into this, and thank you for
> > > >> prompting the ponderance
> > > >> 3) distinct sidewalls back-to-back in the middle of a space without
> a
> > > >> baffle or beam to prevent cold soldering is a no go I realize now,
> but
> > > with
> > > >> a baffle or beam the head on the opposite side of the ignition point
> > > might
> > > >> not activate due to the way the ceiling jet hits the beam, goes
> under
> > > it,
> > > >> and comes back up the other side-- the opposite side spinkler, being
> > > above
> > > >> the bottom and close to the side of the beam leaves it in a "slow
> and
> > > cold
> > > >> pocket".
> > > >> The best thing would be a Tyco type back to back attic head, (2
> > > sidewalls
> > > >> with one element) but they would have to bend both deflectors up to
> > work
> > > >> with a flat ceiling :) unless the ceiling height was up there a
> ways.
> > > >> 4) seems like you guys there at Aero are really on the ball!!!--
> prime
> > > >> candidates for some serious fire modeling.  .  .
> > >
> > > >> wbr, Brad
> > > >> On Dec 22, 2015 5:05 PM, "Brad Casterline" <[email protected]>
> > > wrote:
> > >
> > > >> > *coarse. And an 18" deep draft stop is for containing smoke, not
> to
> > > >> > enhance sprinkler activation, and, I apologise for not knowing how
> > to
> > > >> trim
> > > >> > threads when at home using my phone.
> > > >> > On Dec 22, 2015 4:48 PM, "Brad Casterline" <
> [email protected]>
> > > >> wrote:
> > > >> >
> > > >> >> No better subject to ramble on about than sprinkler activation.
> > > >> >> I think citing sidewalls under an overhead door is misplaced
> though
> > > >> >> because in that case there is an 'above AND below' setup, and
> > whether
> > > >> the
> > > >> >> door is up or down the fire has to be pretty much right under the
> > > >> 'exposed
> > > >> >> sidewall'. Not so with one compliment.
> > > >> >> If you did the back-to-back sidewalls in the middle of the space
> I
> > > would
> > > >> >> advocate no wall, baffle, or beam, that being based on some
> > > primitive,
> > > >> >> course modeling I did several years ago looking at activation
> times
> > > for
> > > >> >> water curtains with and without a draft stop: with seemed to 1)
> > slow
> > > the
> > > >> >> velocity of the ceiling jet a tad and 2) block half the pattern--
> > > RTI is
> > > >> >> based on temp AND velocity.
> > > >> >>
> > > >> >> I've been modeling this all afternoon in my mind because I
> skated a
> > > >> >> little early today-
> > > >> >> I'll actually do it I'm sure, soon, make a youtube movie, and
> post
> > > the
> > > >> >> link to that here-- but, you should resign yourself, re. any real
> > > life
> > > >> >> application to using a sideWALL  essentially with a 'wall' :) ;)
> :)
> > > >> >>
> > > >> >> B-rad
> > > >> >> On Dec 22, 2015 11:54 AM, <[email protected]> wrote:
> > > >> >>
> > > >> >>> Thank you Richard and Brad.
> > > >> >>>
> > > >> >>> These are some of the exact points I was looking at/for.  Up to
> > this
> > > >> >>> point we had only used them under garage doors.  But like Duane
> > > >> brought up,
> > > >> >>> we were wondering if they can be installed under garage doors
> and
> > be
> > > >> >>> expected to operate, then shouldn't they also be allowed to be
> > > >> installed in
> > > >> >>> "exposed" scenarios.  Maybe this just one of those "calculated
> > > risks"
> > > >> by
> > > >> >>> the committee if no other testing has been done.
> > > >> >>>
> > > >> >>> Moving on, so if I follow 8.7.4.1.2.2, and located the deflector
> > > >> >>> accordingly off the "wall".  What are the other defining
> > > >> characteristics of
> > > >> >>> this "wall"?  How deep is it?  How long does it have to be?  As
> > far
> > > as
> > > >> I
> > > >> >>> know "wall" isn't defined in Chapter 3.  You may laugh and
> think I
> > > am
> > > >> going
> > > >> >>> too far with this, but one of the major sprinkler manufactures
> > > states
> > > >> the
> > > >> >>> following in one of their product listings "Horizontal sidewall
> > > >> sprinklers
> > > >> >>> are designed for installation along a wall or the side of a
> beam".
> > > >> Since
> > > >> >>> they are clearly indicating beams are acceptable for proper
> > > operation,
> > > >> can
> > > >> >>> I assume "wall" in 8.7.4.1.2.2 doesn't mean it has to run from
> > > floor to
> > > >> >>> ceiling.  From this point going forward I can see someone
> arguing
> > > from
> > > >> (6)
> > > >> >>> different routes, some of which could be considered "educated
> > > guesses".
> > > >> >>> First (2) should be completely acceptable but not preferred,
> Next
> > > (3)
> > > >> have
> > > >> >>> their pros/cons and varying degrees of applicability, last (1)
> is
> > > the
> > > >> most
> > > >> >>> preferred but probably won't be
> > > >> >>>  accepted.
> > > >> >>>
> > > >> >>> (1) Build a wall.
> > > >> >>> (2) Install a beam.
> > > >> >>> (3) Use the definition of Compartment from 3.3.6.  A sidewall
> can
> > be
> > > >> >>> installed in a "compartment", so an 8" lintel should be
> > sufficient.
> > > >> Since
> > > >> >>> the 8" lintel allows a maximum opening of 8ft in the wall, space
> > the
> > > >> heads
> > > >> >>> every 8ft and run the lintel the length of the sidewalls.
> > > >> >>> (4) Use the definition of Draft Curtain from 8.4.6.4.1.  Since
> > this
> > > is
> > > >> >>> acceptable to separate sprinklers with different response times,
> > it
> > > >> will
> > > >> >>> clearly delay the heat travel long enough for a sprinkler to
> > > operate.
> > > >> This
> > > >> >>> would require a barrier 2ft deep running the length of the
> > > >> sprinklers.  No
> > > >> >>> apparent restriction on sprinkler spacing.
> > > >> >>> (5) Use the definition of Draft Stop from 8.15.4.2.  Since this
> is
> > > >> >>> acceptable to delay heat traveling vertically from floor to
> floor.
> > > >> This
> > > >> >>> would require a barrier 18in deep with heads spaced 6ft apart.
> > > >> >>> (6) If we decide the wall/beam isn't required to be a heat trap,
> > but
> > > >> >>> rather a protection of spray from other sprinklers.  Use the
> > > >> definition for
> > > >> >>> Baffles with Sidewalls 8.7.3.4.  Baffles are at least 8" long,
> 6"
> > > >> high, be
> > > >> >>> between 2in and 3in above the deflector, and the bottom be at
> > least
> > > >> even
> > > >> >>> with the deflector.
> > > >> >>>
> > > >> >>> Obviously I would like to choose (6) if acceptable.  However do
> > you
> > > see
> > > >> >>> any viability of these (4) "educated guesses"?
> > > >> >>>
> > > >> >>> I appreciate any further input/opinion and of course your time
> to
> > > >> listen
> > > >> >>> to me ramble on.
> > > >> >>>
> > > >> >>> Thanks,
> > > >> >>> Sean VG
> > > >> >>>
> > > >> >>>
> > > >> >>>
> > > >> >>> -----Original Message-----
> > > >> >>> From: Sprinklerforum [mailto:
> > > >> >>> [email protected]] On Behalf Of
> Brad
> > > >> >>> Casterline
> > > >> >>> Sent: Tuesday, December 22, 2015 9:58 AM
> > > >> >>> To: [email protected]
> > > >> >>> Subject: RE: can sidewalls be installed when not located next
> to a
> > > >> wall?
> > > >> >>>
> > > >> >>> Sean, I found this in the archives:
> > > >> >>> *****
> > > >> >>> Can a horizontal sidewall sprinkler be installed in the center
> of
> > a
> > > >> room
> > > >> >>> (flat, smooth clg) provided sprinkler coverage is added behind
> the
> > > >> >>> sidewall?  In other words, not installed near a wall or soffit.
> > > >> >>>
> > > >> >>> In reality a sidewall installed 4" to 6" below the ceiling (away
> > > from a
> > > >> >>> wall/soffit) should activate in similar fashion as exposed
> > pendents
> > > and
> > > >> >>> uprights (1" - 12" below clg).  If code permits "exposed"
> > sidewalls
> > > to
> > > >> be
> > > >> >>> installed below roll up doors without soffits, can't an
> "exposed"
> > > >> >>> sidewall be installed elsewhere?
> > > >> >>>
> > > >> >>> Is there anything in the listing of a sidewall that requires the
> > > >> >>> sprinkler be installed on a wall or soffit?  Are there any
> ROP/ROC
> > > >> >>> responses from the committee that would help answer the
> question?
> > > >> >>>
> > > >> >>> Thoughts?
> > > >> >>>
> > > >> >>> Duane Johnson, PE
> > > >> >>> Program Manager
> > > >> >>> Division of the Fire Marshal (Support Contractor) Office of
> > Research
> > > >> >>> Services National Institutes of Health
> > > >> >>> 301-496-0487
> > > >> >>>
> > > >> >>>
> > > >> >>> Duane,
> > > >> >>>
> > > >> >>> NFPA 13(2007) 8.7.4.1.2 addresses the location of vertical and
> > > >> >>> horizontal sidewalls in relation to the wall that they are
> > projected
> > > >> from.
> > > >> >>>
> > > >> >>> Sidewall sprinklers cannot be positioned in the center of a room
> > as
> > > a
> > > >> >>> pendant.
> > > >> >>>
> > > >> >>>
> > > >> >>>
> > > >> >>> Dale F. Wingard, SET
> > > >> >>> Design Manager
> > > >> >>> Triple "A" Fire Protection, Inc.
> > > >> >>> 251.649.2034
> > > >> >>> [email protected]
> > > >> >>>
> > > >> >>>
> > > >> >>> ********
> > > >> >>> Brad
> > > >> >>>
> > > >> >>>
> > > >> >>> -----Original Message-----
> > > >> >>> From: Sprinklerforum [mailto:
> > > >> >>> [email protected]]
> > > >> >>> On Behalf Of Richard Carr
> > > >> >>> Sent: Tuesday, December 22, 2015 10:19 AM
> > > >> >>> To: [email protected]
> > > >> >>> Subject: RE: can sidewalls be installed when not located next
> to a
> > > >> wall?
> > > >> >>>
> > > >> >>> Under overhead doors is only place I know is acceptable without
> a
> > > wall.
> > > >> >>>
> > > >> >>>
> > > >> >>>
> > > >> >>> Sent from my T-Mobile 4G LTE Device
> > > >> >>>
> > > >> >>>
> > > >> >>> -------- Original message --------
> > > >> >>> From: [email protected]
> > > >> >>> Date: 12/22/2015 11:14 AM (GMT-05:00)
> > > >> >>> To: [email protected]
> > > >> >>> Subject: can sidewalls be installed when not located next to a
> > wall?
> > > >> >>>
> > > >> >>> Hi All,
> > > >> >>>
> > > >> >>> I can't check the forum archives right now because the website
> > isn't
> > > >> >>> loading for me for some reason.  Based on NFPA 13 2013.
> > > >> >>>
> > > >> >>> Can sidewalls be installed when not located next to a wall?
> > > >> >>>
> > > >> >>> Assuming we meet the all the minimum/maximum spacing
> requirements,
> > > >> >>> vertical distance below the deck requirements, standard spray
> > > >> sprinklers,
> > > >> >>> ordinary hazard occupancy, noncombustible construction.  Walking
> > > from
> > > >> >>> branchline to branchline left to right, can I install upright,
> > > upright,
> > > >> >>> sidewall facing right, sidewall facing left, upright, upright.
> > With
> > > >> >>> spacing from upright to upright equal to 12ft, spacing from
> > upright
> > > to
> > > >> >>> backside of sidewall of 6ft, and spacing from sidewall face to
> > > sidewall
> > > >> >>> face equal to 20ft.  Is this acceptable?
> > > >> >>>
> > > >> >>> The first thing most people say is "will the sidewall be next to
> > > >> >>> something like a baffle or installed with the pipe in a soffit?"
> > > As of
> > > >> >>> now, no, there is nothing behind the sidewalls.  If something is
> > > >> required,
> > > >> >>> please help me find the direction in the code for this
> requirement
> > > and
> > > >> >>> design parameters.
> > > >> >>> Because right now all I am finding is a lot of "grey" area that
> > > people
> > > >> >>> can interpret whichever way suits their needs.  I'm looking for
> > > "black
> > > >> and
> > > >> >>> white" if it is in there.  If it's only "grey", opinions are
> > greatly
> > > >> >>> appreciated.
> > > >> >>>
> > > >> >>> Thank you for your time and help!
> > > >> >>>
> > > >> >>> Thanks,
> > > >> >>> Sean VG
> > > >> >>>
> > > >> >>>
> > > >> >>>
> > > >> >>>
> > > >> >>>
> > > >> >>> _______________________________________________
> > > >> >>> Sprinklerforum mailing list
> > > >> >>> [email protected]
> > > >> >>>
> > > >> >>>
> > > >>
> > >
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> > > >> >>> _______________________________________________
> > > >> >>> Sprinklerforum mailing list
> > > >> >>> [email protected]
> > > >> >>>
> > > >> >>>
> > > >>
> > >
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> > > >> >>>
> > > >> >>> _______________________________________________
> > > >> >>> Sprinklerforum mailing list
> > > >> >>> [email protected]
> > > >> >>>
> > > >> >>>
> > > >>
> > >
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> > > >> >>> _______________________________________________
> > > >> >>> Sprinklerforum mailing list
> > > >> >>> [email protected]
> > > >> >>>
> > > >> >>>
> > > >>
> > >
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> > > >> >>>
> > > >> >>
> > > >> _______________________________________________
> > > >> Sprinklerforum mailing list
> > > >> [email protected]
> > >
> > > >>
> > >
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> > >
> > > > _______________________________________________
> > > > Sprinklerforum mailing list
> > > > [email protected]
> > > >
> > >
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> > >
> > >
> > >
> > > --
> > > Best regards,
> > >  Charles                            mailto:[email protected]
> > >
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > >
> > >
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> > >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >
>
>
>
> --
> Ron Greenman
> Instructor
> Fire Protection Engineering Technology
> Bates Technical College
> 1101 So. Yakima Ave.
> Tacoma, WA 98405
>
> [email protected]
>
> http://www.bates.ctc.edu/fireprotection/
>
> 253.680.7346
> 253.576.9700 (cell)
>
> Member:
> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
>
> They are happy men whose natures sort with their vocations. -Francis Bacon,
> essayist, philosopher, and statesman (1561-1626)
>
> A problem well stated is a problem half solved. -Charles F. Kettering,
> inventor and engineer (1876-1958)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to