The AHJ is going to have to make the final call. My pay scale isn't high enough to make those types decisions, but if it were, I'd say no. If water spray from the 1st sprinkler or 2 damages the insulation to allow heat to flow past it, you've lost your heat barrier and the 1000 sf design area is out-the-window.
Back to my regularly scheduled program. Ed Kramer Bamford Fire Sprinkler -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Travis Mack, SET Sent: Friday, February 12, 2016 9:28 AM To: [email protected] Subject: Re: Tyco CC sprinklers / draft curtain That is what the contractor is arguing. The NFPA 13 definitions of draft curtains are in reference to separation of ESFR and SR, water spray systems and hazard separation. It is an outside the box thinking for sure. As you say, if it is stapled to the deck, that would prevent heat from passing through and over. That is the only criteria in the datasheet. Travis Mack, SET MFP Design, LLC 2508 E Lodgepole Drive Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 email:[email protected] http://www.mfpdesign.com https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Send large files to us via: https://www.hightail.com/u/MFPDesign On 2/12/2016 8:19 AM, Matthew J Willis wrote: > LOL. > > I say it does meet it. > Insulation by default blocks heat.. > > R/ > Matt > > > Matthew J. Willis > Project Manager > Rapid Fire Protection Inc. > *NEW ADDRESS* > 1530 Samco Road > Rapid City, SD 57702 > Office-605.348.2342 > Direct Line-605.593.5063 > Cell-605.391.2733 > Fax:-605.348.0108 > > > > > > > -----Original Message----- > From: Sprinklerforum > [mailto:[email protected]] On Behalf Of > Travis Mack > Sent: Friday, February 12, 2016 8:16 AM > To: [email protected] > Subject: Re: Tyco CC sprinklers / draft curtain > > Well, the customer called Tyco and they could not say definitively if the insulation would meet the requirements or not. > > > > Travis Mack, SET > MFP Design, LLC > "Follow" us on Facebook: > https://www.facebook.com/pages/MFP-Design-LLC/92218417692 > Send large files to MFP Design via: > https://www.hightail.com/u/MFPDesign > > Sent from my iPhone > >> On Feb 11, 2016, at 4:49 PM, Travis Mack, SET <[email protected]> wrote: >> >> I have a customer that is asking if batt insulation can be secured to the roof decking and used as a draft curtain for the Tyco CC sprinklers. I have never seen an application such as this, but it doesn't seem to be prohibited in the datasheet. The only requirement is that it must be constructed of a material so that heat can not pass through or over. >> >> What do you think? Could insulation secured to the roof/floor deck serve as a draft curtain for these sprinklers? My gut feeling is that it would not be suitable, but I can't find something in the data sheet to support that. My only thought is that activation of a sprinkler could possibly knock the insulation down. >> >> -- >> Travis Mack, SET >> MFP Design, LLC >> 2508 E Lodgepole Drive >> Gilbert, AZ 85298 >> 480-505-9271 >> fax: 866-430-6107 >> email:[email protected] >> >> http://www.mfpdesign.com >> https://www.facebook.com/pages/MFP-Design-LLC/92218417692 >> Send large files to us via: https://www.hightail.com/u/MFPDesign >> >> _______________________________________________ >> Sprinklerforum mailing list >> [email protected] >> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink >> ler.org > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl > er.org > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl > er.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org