For crying out loud though, isn't the max 'ceiling height' for this
application THREE FEET?
On Feb 12, 2016 9:54 AM, "Travis Mack, SET" <[email protected]> wrote:

> You and I are on the same page.  We were just hoping to get a definitive
> answer from the manufacturer.
>
> Travis Mack, SET
> MFP Design, LLC
> 2508 E Lodgepole Drive
> Gilbert, AZ 85298
> 480-505-9271
> fax: 866-430-6107
> email:[email protected]
>
> http://www.mfpdesign.com
> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
> Send large files to us via: https://www.hightail.com/u/MFPDesign
>
> On 2/12/2016 8:53 AM, Ed Kramer wrote:
>
>> The AHJ is going to have to make the final call.  My pay scale isn't high
>> enough to make those types decisions, but if it were,  I'd say no.  If
>> water
>> spray from the 1st sprinkler or 2 damages the insulation to allow heat to
>> flow past it, you've lost your heat barrier and the 1000 sf design area is
>> out-the-window.
>>
>> Back to my regularly scheduled program.
>>
>> Ed Kramer
>> Bamford Fire Sprinkler
>>
>> -----Original Message-----
>> From: Sprinklerforum [mailto:
>> [email protected]]
>> On Behalf Of Travis Mack, SET
>> Sent: Friday, February 12, 2016 9:28 AM
>> To: [email protected]
>> Subject: Re: Tyco CC sprinklers / draft curtain
>>
>> That is what the contractor is arguing.  The NFPA 13 definitions of draft
>> curtains are in reference to separation of ESFR and SR, water spray
>> systems
>> and hazard separation.
>>
>> It is an outside the box thinking for sure.  As you say, if it is stapled
>> to
>> the deck, that would prevent heat from passing through and over.  That is
>> the only criteria in the datasheet.
>>
>>
>> Travis Mack, SET
>> MFP Design, LLC
>> 2508 E Lodgepole Drive
>> Gilbert, AZ 85298
>> 480-505-9271
>> fax: 866-430-6107
>> email:[email protected]
>>
>> http://www.mfpdesign.com
>> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
>> Send large files to us via: https://www.hightail.com/u/MFPDesign
>>
>> On 2/12/2016 8:19 AM, Matthew J Willis wrote:
>>
>>> LOL.
>>>
>>> I say it does meet it.
>>> Insulation by default blocks heat..
>>>
>>> R/
>>> Matt
>>>
>>>
>>> Matthew J. Willis
>>> Project Manager
>>> Rapid Fire Protection Inc.
>>> *NEW ADDRESS*
>>> 1530 Samco Road
>>> Rapid City, SD 57702
>>> Office-605.348.2342
>>> Direct Line-605.593.5063
>>> Cell-605.391.2733
>>> Fax:-605.348.0108
>>>
>>>
>>>
>>>
>>>
>>>
>>> -----Original Message-----
>>> From: Sprinklerforum
>>> [mailto:[email protected]] On Behalf Of
>>> Travis Mack
>>> Sent: Friday, February 12, 2016 8:16 AM
>>> To: [email protected]
>>> Subject: Re: Tyco CC sprinklers / draft curtain
>>>
>>> Well, the customer called Tyco and they could not say definitively if the
>>>
>> insulation would meet the requirements or not.
>>
>>>
>>>
>>> Travis Mack, SET
>>> MFP Design, LLC
>>> "Follow" us on Facebook:
>>> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
>>> Send large files to MFP Design via:
>>> https://www.hightail.com/u/MFPDesign
>>>
>>> Sent from my iPhone
>>>
>>> On Feb 11, 2016, at 4:49 PM, Travis Mack, SET <[email protected]>
>>>>
>>> wrote:
>>
>>> I have a customer that is asking if batt insulation can be secured to the
>>>>
>>> roof decking and used as a draft curtain for the Tyco CC sprinklers.  I
>> have
>> never seen an application such as this, but it doesn't seem to be
>> prohibited
>> in the datasheet.  The only requirement is that it must be constructed of
>> a
>> material so that heat can not pass through or over.
>>
>>> What do you think?  Could insulation secured to the roof/floor deck serve
>>>>
>>> as a draft curtain for these sprinklers?  My gut feeling is that it would
>> not be suitable, but I can't find something in the data sheet to support
>> that.  My only thought is that activation of a sprinkler could possibly
>> knock the insulation down.
>>
>>> --
>>>> Travis Mack, SET
>>>> MFP Design, LLC
>>>> 2508 E Lodgepole Drive
>>>> Gilbert, AZ 85298
>>>> 480-505-9271
>>>> fax: 866-430-6107
>>>> email:[email protected]
>>>>
>>>> http://www.mfpdesign.com
>>>> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
>>>> Send large files to us via: https://www.hightail.com/u/MFPDesign
>>>>
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>>>> ler.org
>>>>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>>> er.org
>>>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>>> er.org
>>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>>
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>>
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to