Do you have positive pressure when testing for 150% capacity?

Mike Hill

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Matt Grise
Sent: Tuesday, February 16, 2016 7:57 AM
To: [email protected]
Subject: RE: Oversized fire pump

That might be a little too low pressure for the water company. 

Matt Grisé PE*, LEED AP, NICET II  
Sales Engineer 
Alliance Fire Protection 
130 w 9th Ave.
North Kansas City, MO 64116

*Licensed in KS & MO 
 
913.888.0647 ph 
913.888.0618 f 
913.526.7443 cell 
www. AFPsprink.com 
 


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Richard Carr
Sent: Tuesday, February 16, 2016 6:52 AM
To: [email protected]
Subject: RE: Oversized fire pump

If you maintaining 18 psi on the suction side with the pump running, why
would you do anything?

Richard Carr, SET
Branch Manager
Cox Fire Protection, Inc
6555 Grace Lane.
Jacksonville, Fl. 32205
[email protected]
904-781-8227

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Matt Grise
Sent: Tuesday, February 16, 2016 7:42 AM
To: [email protected]
Subject: RE: Oversized fire pump

How about a suction control valve?

Matt Grisé PE*, LEED AP, NICET II  
Sales Engineer 
Alliance Fire Protection 
130 w 9th Ave.
North Kansas City, MO 64116

*Licensed in KS & MO 
 
913.888.0647 ph 
913.888.0618 f 
913.526.7443 cell 
www. AFPsprink.com 
 


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Todd Williams
Sent: Tuesday, February 16, 2016 6:41 AM
To: [email protected]
Subject: Oversized fire pump

I am working on a facility with a fire pump that was oversized for the
available public water supply. The pump is 1500 gpm at 85 psi. At 1500 gpm,
the suction pressure drops to 18 psi. This is characteristic of the water
supply and is not due to a shut valve or other obstruction. The pump was
installed in 2009. 
Are
there any safeguards that I should recommend for this situation?

Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT
860-535-2080 (ofc) 860-608-4559 (cell)
Sent using CloudMagic
[https://cloudmagic.com/k/d/mailapp?ct=ti&cv=6.0.64&pv=8.2]
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to