Existing pumps in pits need to be replaced.

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Bruce Verhei
Sent: Wednesday, February 24, 2016 10:54 AM
To: [email protected]
Subject: Re: Fire pump in pit

I've been trying to visualize the why of this installation in the first
instance. It sounds more expensive. 

It would be cheaper to pipe up to a slab, and raised motor mount level than
to form and pour a pit. A designer fix to trying to meet ten diameters of
straight run on inlet side? Move the pump instead of changing pipe layout?

What am I missing?

Best

Bruce Verhei



> On Feb 24, 2016, at 05:08, Tim Stone <[email protected]> wrote:
> 
> Scott, Any argument to get the fire pumps out of the pits.
> 
> Regards,
> G. Tim Stone
> 
> G. Tim Stone Consulting, LLC
> NICET Level III Engineering Technician Fire Protection Sprinkler 
> Design and Consulting Services
> 
>                 117 Old Stage Rd. - Essex Jct., VT. 05452
> CELL: (802) 373-0638   TEL: (802) 434-2968   Fax: (802) 434-4343
>                            [email protected]
> 
> 
> -----Original Message-----
> From: Sprinklerforum 
> [mailto:[email protected]]
> On Behalf Of Scott Futrell
> Sent: Wednesday, February 24, 2016 7:59 AM
> To: [email protected]
> Subject: RE: Fire pump in pit
> 
> 
> Tim, I'm not sure exactly what that standard states, but I can't 
> imagine not complying with all of the confined space entry 
> requirements prior to entering a below ground fire pump pit for work 
> or testing. Just because a pit is existing doesn't mean the same 
> hazards don't apply or that someone won't get hurt operating or testing a
fire pump or equipment.
> 
> I would say the combination of NFPA 20 and OSHA requirements would 
> seal the deal.
> 
> Scott
> 
> Office: (763) 425-1001 x 202
> Cell: (612) 759-5556
> 
> -----Original Message-----
> From: Sprinklerforum 
> [mailto:[email protected]]
> On Behalf Of Tim Stone
> Sent: Wednesday, February 24, 2016 6:50 AM
> To: [email protected]
> Subject: RE: Fire pump in pit
> 
> Document OSHA 1910, "existing confined spaces"
> As john and I both mentioned, NFPA 20 should provide enough 
> information to get the pumps out of the pits.
> 
> Regards,
> G. Tim Stone
> 
> G. Tim Stone Consulting, LLC
> NICET Level III Engineering Technician Fire Protection Sprinkler 
> Design and Consulting Services
> 
>                 117 Old Stage Rd. - Essex Jct., VT. 05452
> CELL: (802) 373-0638   TEL: (802) 434-2968   Fax: (802) 434-4343
>                            [email protected]
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to