Ed,

I think the only thing special about a COIN-type sprinkler is that, if
spaced (and calc'd) correctly the patterns will overlap in a shallow depth.
So if I were King, or better yet an AHJ, I would accept room design.

Brad
On Mar 14, 2016 5:25 PM, "Ed Kramer" <[email protected]> wrote:

> Working on a project where listed combustible concealed space sprinklers
> (such as Viking COIN) are required.  Data sheets call for a design area of
> 1,000 sf.  However, the combustible concealed spaces on several floors of
> this motel are compartmented into areas of approx 345 sf via 1-hour rated
> walls.  A 1,000 sf design area would include  up to 8 sprinklers, whereas a
> design area  of (1) 1-hour rated compartment would include only 3
> sprinklers.  I'd love to use the room design method and calc only 3
> sprinklers, but since these are specially listed sprinklers and the listing
> calls for 1,000 sf, I don't believe I'm allowed to do that.  Anybody else
> run into this or have an opinion?
>
>
>
> Ed Kramer
>
> Bamford Fire Sprinkler
>