In my opinion you're going to have to stick to manufacturer listing for
these. I don't know of any type of exception. Fortunately they're only 4.2K
factor so chances are, if this is a 13 system, your pendants will more than
likely still be the driving factor depending on spacing and layout - even
though they're only four in the design area.

On Mon, Mar 14, 2016 at 3:39 PM, Brad Casterline <[email protected]>
wrote:

> Ed,
>
> I think the only thing special about a COIN-type sprinkler is that, if
> spaced (and calc'd) correctly the patterns will overlap in a shallow depth.
> So if I were King, or better yet an AHJ, I would accept room design.
>
> Brad
> On Mar 14, 2016 5:25 PM, "Ed Kramer" <[email protected]> wrote:
>
> > Working on a project where listed combustible concealed space sprinklers
> > (such as Viking COIN) are required.  Data sheets call for a design area
> of
> > 1,000 sf.  However, the combustible concealed spaces on several floors of
> > this motel are compartmented into areas of approx 345 sf via 1-hour rated
> > walls.  A 1,000 sf design area would include  up to 8 sprinklers,
> whereas a
> > design area  of (1) 1-hour rated compartment would include only 3
> > sprinklers.  I'd love to use the room design method and calc only 3
> > sprinklers, but since these are specially listed sprinklers and the
> listing
> > calls for 1,000 sf, I don't believe I'm allowed to do that.  Anybody else
> > run into this or have an opinion?
> >
> >
> >
> > Ed Kramer
> >
> > Bamford Fire Sprinkler
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to