Design requirements are in NFPA 30.
How high is storage?

Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell



-----Original Message-----
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of James Crawford
Sent: Wednesday, March 30, 2016 1:15 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Class IIIB Liquid Storage

A client has a building that is protected with an Ordinary Hazard Group 3
system.

 

They want to store class IIIB combustible liquids in 16 gal and 55 gal
drums.

 

Table 9.6.1 gives the MAQ for a IIIB as 13,200 gal with note 1 & 4 and note
4 states that the quantities are not limited if the building is equipped
with an automatic sprinkler system installed in accordance with NFPA #13.
This seems to imply that they could store an unlimited amount of class IIIB
liquids.

 

Table 12.6.2.2 gives the MAQ as 55,000 gal if the building is protected with
a sprinkler system designed for class 4 commodities to 20'.

 

Am I missing something

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

 

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to