Design requirements are in NFPA 30. How high is storage?
Art Tiroly ATCO Fire Protection/Tiroly 24400 Highland Rd CLE 44143 216-621-8899 216-570-7030 cell -----Original Message----- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of James Crawford Sent: Wednesday, March 30, 2016 1:15 PM To: sprinklerforum@lists.firesprinkler.org Subject: Class IIIB Liquid Storage A client has a building that is protected with an Ordinary Hazard Group 3 system. They want to store class IIIB combustible liquids in 16 gal and 55 gal drums. Table 9.6.1 gives the MAQ for a IIIB as 13,200 gal with note 1 & 4 and note 4 states that the quantities are not limited if the building is equipped with an automatic sprinkler system installed in accordance with NFPA #13. This seems to imply that they could store an unlimited amount of class IIIB liquids. Table 12.6.2.2 gives the MAQ as 55,000 gal if the building is protected with a sprinkler system designed for class 4 commodities to 20'. Am I missing something Thank you James Crawford Phaser Fire Protection Ltd. Phone 604-888-0318 Fax 604-888-4732 Cel 604-790-0938 Email jcrawf...@phaserfire.ca _______________________________________________ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org --- This email has been checked for viruses by Avast antivirus software. https://www.avast.com/antivirus _______________________________________________ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org