>From NFPA 1:13.3.3.3 Ceiling Tiles and Ceiling Assemblies. Where automatic 
>sprinklers are installed, ceilings necessary for the proper actuation of the 
>fire protection device in accordance with NFPA 13 shall be maintained.

Duane

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of John Allen, CET, CFPS
Sent: Thursday, March 31, 2016 9:40 AM
To: [email protected]
Subject: RE: Missing ceiling tiles

This is the code we use to support our findings:

NFPA 101 (2012) 8.5.6.4    Where sprinklers penetrate a single membrane of a 
fire resistance rated assembly in buildings equipped throughout with an 
approved automatic fire sprinkler system, noncombustible escutcheon plates 
shall be permitted, provided that the space around each sprinkler penetration 
does not exceed 1/2 in. (13 mm), measured between the edge of the membrane and 
the sprinkler.

Best Regards,
 
John Allen, CET, CFPS
President



AFS: Allen Fire & Security
Your Safety is Our Success
Direct: 770.715.7261 | Office: 770.723.7280 Ext 2 | Fax: 678.894.4180 
 

  Please consider the environment before printing this email This email 
contains proprietary and confidential material for the sole use of the intended 
recipient and is the sole property of AFS.  Any review, use, distribution or 
disclosure by others without the permission of the sender is strictly 
prohibited. If you are not the intended recipient (or authorized to receive for 
the recipient), please contact the sender by reply email and delete all copies 
of the message.



-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of michael G
Sent: Thursday, March 31, 2016 9:08 AM
To: [email protected]
Subject: RE: Missing ceiling tiles

As a general rule we have always noted if there is missing tile in the room, 
(near the edges away from the sprinklers. I know that I have always written it 
up as a deficiency if the tile was out within a 5ft area around the sprinkler. 
if it's a small closet or storage room and its missing a tile or two, then I 
have written it down as a deficiency as well due to the potential for the heat 
loss not allowing for the activation of the sprinkler.

 As for the missing escutcheons, (this is my opinion) I don't see why they 
wouldn't be a critical deficiency due to the listings on the sprinklers.
The sprinklers are listed with the plate to be installed in the manner for the 
plate that it was installed with ( recessed, flush, Concealed, 401).  

But you are definitely correct in the statement that this is a gray area in 
NFPA #25.  I guess if we step back and think about the original installation of 
the ceilings and sprinklers, when the system was bought off by the fire 
marshal, wasn't it required to have all the tile in at the time of his walk 
through? So why wouldn't the building still be required to have all the tiles 
in place on a NFPA 25 inspection.

Michael Goodis
Estimator, Project Manager
IL#000635   NICET#135586
Key Fire Protection Enterprises LLC
3200 Mike Padgett HWY
Augusta, GA 30906
Office- (706)790-3473
Cell- (706) 220-8822
Fax: (706) 738-2119



-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Jay Stough
Sent: Thursday, March 31, 2016 8:33 AM
To: Sprinkler Forum
Subject: Missing ceiling tiles

We are having a discussion as to whether missing ceiling tiles are a deficiency 
in NFPA 25.  It does not specifically mention it, but it is a non-critical 
deficiency if it is missing escutcheons and cover plates on semi-recessed, 
recessed and concealed sprinklers.  Wouldn't missing ceiling tiles create the 
same problem in a room with a drop ceiling?  I would think it would really 
screw up the air flow of heat to the sprinklers if there are 2' X 2' or 2' X 4' 
holes in the ceilings.

*Jay Stough*
NICET IV LAYOUT
NICET III ITM
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to