I don't see how I can cite the building code, fire code or NFPA 101 if I am
doing an NFPA 25 inspection.  And as far as allowing openings in the
ceiling, I am sure there are no sprinklers above the ceiling or that the
tiles are removed due to the reasons cited in 13.  I guess the best way to
denote it is as a change in the building per chapter 4 since the code or
fire official probably did not accept the building with missing tiles or
they were not missing last year.

*Jay Stough*
NICET IV LAYOUT
NICET III ITM

On Thu, Mar 31, 2016 at 2:08 PM, Larrimer, Peter A <[email protected]>
wrote:

> John,
>
> I am not sure what your finding is, but I would be careful  when trying to
> use that for a missing escutcheon for a sprinkler.  That paragraph in NFPA
> 101 allows a penetration (of a pipe likely) in a smoke barrier that has a
> fire resistance rating to be sealed by an non-combustible escutcheon plate
> provided the gap around the pipe isn't greater than 1/2 inch.  It would
> only apply if the barrier was a smoke barrier with a fire resistance rating
> and it is a membrane protection (one side of the wall) and it wouldn't
> actually require an escutcheon plate.  That paragraph in NFPA 101 will
> likely not be a very helpful reference when trying to require a sprinkler
> to have an escutcheon.  Hope this helps.
>
> Thanks
>
> Pete Larrimer
> VA
>
>
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> [email protected]] On Behalf Of John Allen,
> CET, CFPS
> Sent: Thursday, March 31, 2016 9:40 AM
> To: [email protected]
> Subject: [EXTERNAL] RE: Missing ceiling tiles
>
> This is the code we use to support our findings:
>
> NFPA 101 (2012) 8.5.6.4    Where sprinklers penetrate a single membrane of
> a fire resistance rated assembly in buildings equipped throughout with an
> approved automatic fire sprinkler system, noncombustible escutcheon plates
> shall be permitted, provided that the space around each sprinkler
> penetration does not exceed 1/2 in. (13 mm), measured between the edge of
> the membrane and the sprinkler.
>
> Best Regards,
>
> John Allen, CET, CFPS
> President
>
>
>
> AFS: Allen Fire & Security
> Your Safety is Our Success
> Direct: 770.715.7261 | Office: 770.723.7280 Ext 2 | Fax: 678.894.4180
>
>
>   Please consider the environment before printing this email This email
> contains proprietary and confidential material for the sole use of the
> intended recipient and is the sole property of AFS.  Any review, use,
> distribution or disclosure by others without the permission of the sender
> is strictly prohibited. If you are not the intended recipient (or
> authorized to receive for the recipient), please contact the sender by
> reply email and delete all copies of the message.
>
>
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> [email protected]] On Behalf Of michael G
> Sent: Thursday, March 31, 2016 9:08 AM
> To: [email protected]
> Subject: RE: Missing ceiling tiles
>
> As a general rule we have always noted if there is missing tile in the
> room, (near the edges away from the sprinklers. I know that I have always
> written it up as a deficiency if the tile was out within a 5ft area around
> the sprinkler. if it's a small closet or storage room and its missing a
> tile or two, then I have written it down as a deficiency as well due to the
> potential for the heat loss not allowing for the activation of the
> sprinkler.
>
>  As for the missing escutcheons, (this is my opinion) I don't see why they
> wouldn't be a critical deficiency due to the listings on the sprinklers.
> The sprinklers are listed with the plate to be installed in the manner for
> the plate that it was installed with ( recessed, flush, Concealed, 401).
>
> But you are definitely correct in the statement that this is a gray area
> in NFPA #25.  I guess if we step back and think about the original
> installation of the ceilings and sprinklers, when the system was bought off
> by the fire marshal, wasn't it required to have all the tile in at the time
> of his walk through? So why wouldn't the building still be required to have
> all the tiles in place on a NFPA 25 inspection.
>
> Michael Goodis
> Estimator, Project Manager
> IL#000635   NICET#135586
> Key Fire Protection Enterprises LLC
> 3200 Mike Padgett HWY
> Augusta, GA 30906
> Office- (706)790-3473
> Cell- (706) 220-8822
> Fax: (706) 738-2119
>
>
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> [email protected]]
> On Behalf Of Jay Stough
> Sent: Thursday, March 31, 2016 8:33 AM
> To: Sprinkler Forum
> Subject: Missing ceiling tiles
>
> We are having a discussion as to whether missing ceiling tiles are a
> deficiency in NFPA 25.  It does not specifically mention it, but it is a
> non-critical deficiency if it is missing escutcheons and cover plates on
> semi-recessed, recessed and concealed sprinklers.  Wouldn't missing ceiling
> tiles create the same problem in a room with a drop ceiling?  I would think
> it would really screw up the air flow of heat to the sprinklers if there
> are 2' X 2' or 2' X 4' holes in the ceilings.
>
> *Jay Stough*
> NICET IV LAYOUT
> NICET III ITM
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to