According to my spread sheet you could get ~195 GPM, based on 10 ft of
1.25" pipe, 1 angle valve, 1 tee (connection to riser) 1 ell, and 1 45.
This would be using the main drain for the forward flow.

Brad
On Apr 26, 2016 12:23 PM, "Matt Grise" <[email protected]> wrote:

> How low can you go with a hose monster with a 1.25" insert (don't have my
> chart handy)
>
> Matt Grisé PE*, LEED AP, NICET II
> Sales Engineer
> Alliance Fire Protection
> 130 w 9th Ave.
> North Kansas City, MO 64116
>
> *Licensed in KS & MO
>
> 913.888.0647 ph
> 913.888.0618 f
> 913.526.7443 cell
> www. AFPsprink.com
>
>
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> [email protected]] On Behalf Of James
> Crawford
> Sent: Tuesday, April 26, 2016 12:16 PM
> To: [email protected]
> Subject: Forward Flow for a Backflow Preventer
>
> I know this has been discussed but can't seem to find it.
>
>
>
> NFPA #13 (2013) 8.17.4.6.1 Means shall be provided downstream of all
> backflow prevention valves for flow tests at system demand.
>
>
>
> We have a small office system, system demand 160 gpm, we have 100 psi
> static pressure, the system has a 2 ½" riser so a 1 ¼" drain, how much
> water can we get out of an 1 ¼" drain?
>
>
>
> Is there anything out there to help determine the size and or number of
> outlets required to forward flow at different system demands?
>
>
>
>
>
> Thank you
>
>
>
>
>
> James Crawford
>
> Phaser Fire Protection Ltd.
>
> Phone  604-888-0318
>
> Fax 604-888-4732
>
> Cel 604-790-0938
>
> Email  [email protected]
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to