here is link to archived post I made last July.

I changed the English version to show how I got ~195 gpm.

I used the Article Roland mentioned as a way forward, and for checking (and
correcting) my thinking as I went along.

In the text of the post is some brief 'instructions' for zeroing in on the
estimated flow.

I know it appears unorthodox, but all I did is break the Darcy-Weisbach fl
formula down to its simplest form (using ft, ft^2, ft^3, sec, and sec^2).
In order for me to be able to understand anything it has to be in a form
where it could not be any simpler.

If you or any other Forumite wants, I could send the spreadsheet directly to
you. NOTE- it has not been QC'd by anyone other than myself, nor have I
gotten any feedback whatsoever, but I did post my progress, mistakes,
thinking, etc., here, as I went.

Brad  





-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Brad Casterline
Sent: Tuesday, April 26, 2016 12:49 PM
To: [email protected]
Subject: RE: Forward Flow for a Backflow Preventer

According to my spread sheet you could get ~195 GPM, based on 10 ft of
1.25" pipe, 1 angle valve, 1 tee (connection to riser) 1 ell, and 1 45.
This would be using the main drain for the forward flow.

Brad
On Apr 26, 2016 12:23 PM, "Matt Grise" <[email protected]> wrote:

> How low can you go with a hose monster with a 1.25" insert (don't have my
> chart handy)
>
> Matt Grisé PE*, LEED AP, NICET II
> Sales Engineer
> Alliance Fire Protection
> 130 w 9th Ave.
> North Kansas City, MO 64116
>
> *Licensed in KS & MO
>
> 913.888.0647 ph
> 913.888.0618 f
> 913.526.7443 cell
> www. AFPsprink.com
>
>
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> [email protected]] On Behalf Of James
> Crawford
> Sent: Tuesday, April 26, 2016 12:16 PM
> To: [email protected]
> Subject: Forward Flow for a Backflow Preventer
>
> I know this has been discussed but can't seem to find it.
>
>
>
> NFPA #13 (2013) 8.17.4.6.1 Means shall be provided downstream of all
> backflow prevention valves for flow tests at system demand.
>
>
>
> We have a small office system, system demand 160 gpm, we have 100 psi
> static pressure, the system has a 2 ½" riser so a 1 ¼" drain, how much
> water can we get out of an 1 ¼" drain?
>
>
>
> Is there anything out there to help determine the size and or number of
> outlets required to forward flow at different system demands?
>
>
>
>
>
> Thank you
>
>
>
>
>
> James Crawford
>
> Phaser Fire Protection Ltd.
>
> Phone  604-888-0318
>
> Fax 604-888-4732
>
> Cel 604-790-0938
>
> Email  [email protected]
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to