It is determined by condition and voltage.

70 is the place to look.

R/
Matt

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Mike Stossel
Sent: Thursday, May 12, 2016 8:48 AM
To: [email protected]
Subject: Fire Pump Panel

Can anyone confirm the clear space required in front of a fire pump panel?  In 
NFPA 70 it appears to be 3"0", but I would like to confirm that before I tell 
the client their room is too small.

Thanks,