Dear Mike
Consider the controller/panel door opening in full swing and allow space(2.5ft) 
for a person to stand, which counts for the space requirement as a normal case 
for maintenance purpose.

With warm regards

D.RADHAKRISHNAN
Manager-
​Design
 & Engg
UNISAFE FIRE PROTECTION SPECIALISTS LLC
DUBAI, UAE
Mobile: 00971 55 967 4864<tel:00971%2055%20967%204864><mailto:[email protected]>

On Thu, May 12, 2016 at 6:48 PM, Mike Stossel 
<[email protected]<mailto:[email protected]>> wrote:
Can anyone confirm the clear space required in front of a fire pump panel?  In 
NFPA 70 it appears to be 3”0”, but I would like to confirm that before I tell 
the client their room is too small.

Thanks,

<image001.jpg>


   Mike Stossel SET
   NICET Level IV
   Automatic Sprinkler System Layout
   1070 38th Street
   Brooklyn N.Y. 11219
   Office: 718-633-3036 ext 114
   Fax:      718-633-4593
   [email protected]<mailto:[email protected]>
  www.safetyfiresprinkler.com<mailto:[email protected]>


_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to