Dear Mike Consider the controller/panel door opening in full swing and allow space(2.5ft) for a person to stand, which counts for the space requirement as a normal case for maintenance purpose.
With warm regards *D.RADHAKRISHNAN* Manager- Design & Engg *UNISAFE** FIRE PROTECTION SPECIALISTS LLC* DUBAI, UAE Mobile: 00971 55 967 4864 <[email protected]> On Thu, May 12, 2016 at 6:48 PM, Mike Stossel <[email protected]> wrote: > Can anyone confirm the clear space required in front of a fire pump > panel? In NFPA 70 it appears to be 3”0”, but I would like to confirm that > before I tell the client their room is too small. > > > > Thanks, > > > > [image: cid:[email protected]] > > > > > > *Mike Stossel **SET* > > * NICET Level IV* > > * Automatic Sprinkler System Layout* > > * 1070 38th Street* > > * Brooklyn N.Y. 11219* > > * Office: 718-633-3036 ext 114* > > * Fax: 718-633-4593* > > [email protected] > > www.safetyfiresprinkler.com <[email protected]> > > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > >