Dear Mike
Consider the controller/panel door opening in full swing and allow
space(2.5ft) for a person to stand, which counts for the space requirement
as a normal case for maintenance purpose.

With warm regards

*D.RADHAKRISHNAN*
Manager-
​Design
 & Engg
*UNISAFE** FIRE PROTECTION SPECIALISTS LLC*
DUBAI, UAE
Mobile: 00971 55 967 4864 <[email protected]>

On Thu, May 12, 2016 at 6:48 PM, Mike Stossel <[email protected]>
wrote:

> Can anyone confirm the clear space required in front of a fire pump
> panel?  In NFPA 70 it appears to be 3”0”, but I would like to confirm that
> before I tell the client their room is too small.
>
>
>
> Thanks,
>
>
>