Si Senor,
For your POZ-LOK piping system I will try to leave it as is and try to
connect one time and run regular screwed or grooved system whatever is
required the run a quick calc to make sure it works.

Cheers
Walter



On Thu, May 19, 2016 at 8:43 AM, <[email protected]> wrote:

> Greetings to All From New Mexico:
>
> I have a Client (hotel) with a wet-pipe fire sprinkler system, two floors,
> all POZ-LOK pipe and 'fittings'. Transitioning from Hampton Inn to Marriott
> format. Can anyone offer input/ comments about *keeping *the POZ-LOK in
> place while, at same time, is anyone aware of where said pipe and fittings
> might be purchased or is it all "gone"?? Some revisions to the system will
> be required for new walls/ceilings, etc., thus, Owner needs to be able to
> procure parts.
>
> Any and all responses will be most welcome. Obviously, we are trying to
> avoid removing the entire system and 'starting over'.
>
> Gracias from Nuevo Mejico!!
>
> Jerry
> [email protected]
>
> Jerry D. Watts, MSFPE
> President & Co-Founder
> ACCENT FIRE ENGINEERING INT'L. Ltd.
> Santa Fe, New Mexico USA
> (800) 503.1961 nationwide
>
>
>
> In a message dated 5/13/2016 2:27:47 P.M. Mountain Daylight Time,
> [email protected] writes:
>
> Tim,
>
>
>
> There are some NFPA13 R pump manufacturers that have a fire pump skid and
> tank assemblies for NFPA 13-R water supplies.
>
>
>
> Regards
>
>
>
>
>
>
>
> *Davidson Associates*
>
> *Fire Protection Engineering
>
> P. O. Box 4002*
>
> *Code Consultants
>
> Greenville, DE  19807*
>
> *
> (302) 994-9500*
>
> *
> Fax (302) 994-3414*
>
>
>
> *CONFIDENTIALITY*
>
> *This report and any attachments are confidential and also may be
> privileged.*
>
> *If you are not the named recipient, or have otherwise received this
> report in error, please destroy the report, notify the sender immediately,
> and do not disclose its contents to any other person, use them for any
> purpose, or store or copy them in any medium.*
>
> *Thank you for your cooperation.*
>
>
>
> *From:* Sprinklerforum [mailto:
> [email protected]] *On Behalf Of *Tim Stone
> *Sent:* Friday, May 13, 2016 10:16 AM
> *To:* [email protected]
> *Subject:* Polyethylene Tanks
>
>
>
> Are there any requirements in NFPA 22 not allowing the use of Polyethylene
> water storage tanks for residential or commercial sprinkler systems? These
> tanks are installed above ground usually in Basements.
>
> The local State agency is getting ready to adopt the 2013 edition of NFPA
> 22 and I am being told NFPA 22 only permits Fiberglass. I don’t see where
> Polyethylene is excluded.
>
>
>
> Thoughts please.
>
>
>
> Regards,
>
> *G. Tim Stone*
>
>
>
> *G. Tim Stone Consulting, LLC*
>
> *NICET Level III Engineering Technician*
>
> *Fire Protection Sprinkler Design*
>
> *and Consulting Services*
>
>
>
> *                117 Old Stage Rd. - Essex Jct., VT. 05452*
>
> *CELL: (802) 373-0638   TEL: (802) 434-2968   Fax: (802) 434-4343*
>
>                            [email protected]
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to