Recalled years ago. No longer produced or accepted due to the use of schedule 5 
pipe.

"For I am not ashamed of the gospel, because it is God's power for salvation to 
everyone who believes..." HCS Romans 1:16 
"Therefore having overlooked the times of ignorance, God is now declaring to 
men that all people everywhere should repent,..." NASB Acts 17:30

> On May 18, 2016, at 5:43 PM, [email protected] wrote:
> 
> Greetings to All From New Mexico:
>  
> I have a Client (hotel) with a wet-pipe fire sprinkler system, two floors, 
> all POZ-LOK pipe and 'fittings'. Transitioning from Hampton Inn to Marriott 
> format. Can anyone offer input/ comments about keeping the POZ-LOK in place 
> while, at same time, is anyone aware of where said pipe and fittings might be 
> purchased or is it all "gone"?? Some revisions to the system will be required 
> for new walls/ceilings, etc., thus, Owner needs to be able to procure parts.
>  
> Any and all responses will be most welcome. Obviously, we are trying to avoid 
> removing the entire system and 'starting over'.
>  
> Gracias from Nuevo Mejico!!
>  
> Jerry
> [email protected]
>  
> Jerry D. Watts, MSFPE
> President & Co-Founder
> ACCENT FIRE ENGINEERING INT'L. Ltd.
> Santa Fe, New Mexico USA
> (800) 503.1961 nationwide
>  
>  
>  
> In a message dated 5/13/2016 2:27:47 P.M. Mountain Daylight Time, 
> [email protected] writes:
> Tim,
> 
>  
> 
> There are some NFPA13 R pump manufacturers that have a fire pump skid and 
> tank assemblies for NFPA 13-R water supplies.
> 
>  
> 
> Regards
> 
>  
> 
>  
> 
>  
> 
> Davidson Associates
> 
> 
> Fire Protection Engineering                                                   
>                                                                               
>            P. O. Box 4002
> 
> Code Consultants                                                              
>                                                                               
>     Greenville, DE  19807
> 
>                                                                               
>                                                                               
>                            (302) 994-9500
> 
>                                                                               
>                                                                               
>                     Fax (302) 994-3414
> 
>  
> 
> CONFIDENTIALITY
> 
> This report and any attachments are confidential and also may be privileged.
> 
> If you are not the named recipient, or have otherwise received this report in 
> error, please destroy the report, notify the sender immediately, and do not 
> disclose its contents to any other person, use them for any purpose, or store 
> or copy them in any medium.
> 
> Thank you for your cooperation.
> 
>  
> 
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of Tim Stone
> Sent: Friday, May 13, 2016 10:16 AM
> To: [email protected]
> Subject: Polyethylene Tanks
> 
>  
> 
> Are there any requirements in NFPA 22 not allowing the use of Polyethylene 
> water storage tanks for residential or commercial sprinkler systems? These 
> tanks are installed above ground usually in Basements.
> 
> The local State agency is getting ready to adopt the 2013 edition of NFPA 22 
> and I am being told NFPA 22 only permits Fiberglass. I don’t see where 
> Polyethylene is excluded.
> 
>  
> 
> Thoughts please.
> 
>  
> 
> Regards,
> 
> G. Tim Stone
> 
>  
> 
> G. Tim Stone Consulting, LLC
> 
> NICET Level III Engineering Technician
> 
> Fire Protection Sprinkler Design
> 
> and Consulting Services
> 
>  
> 
>                 117 Old Stage Rd. - Essex Jct., VT. 05452
> 
> CELL: (802) 373-0638   TEL: (802) 434-2968   Fax: (802) 434-4343
> 
>                            [email protected]
> 
>  
> 
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to