Russell,

Yes, I used FDS-SMV, a full 3-D 'field model', open source software from
the U.S. government  (NIST).
It is centered in the x,y directions of a .05m by 2m gap, and z dimension
is .025m below the gap. So the ceiling jet crosses (2) panels, width-wise,
with no sprinklers in them. Basically the presence of the gaps for the
small piece I modelled delayed the activation by 5 seconds only.

thanks,

Brad
On May 30, 2016 3:31 AM, "Russell & Carol Gregory" <[email protected]>
wrote:

> Brad,
>
> Does that calculation differentiate where the sprinkler head is located?
> In the gap???? Or just any where on the plane of ceiling.
>
>
>
> Regards,
>
> Russell Gregory
>
> Christchurch,
>
> New Zealand
>
>
>
> *From:* Sprinklerforum [mailto:
> [email protected]] *On Behalf Of *Brad
> Casterline
> *Sent:* Monday, 30 May 2016 11:12 AM
> *To:* [email protected]
> *Subject:* RE: Cloud ceilings & sprinklers in gaps
>
>
>
> Excellent post Nicky; very good questions and observations.
> I agree with what Mark S. said and suggest a few additional considerations:
> 1) Use QR 155F cloud level sprinklers spaced slightly closer than the
> plenum spinklers.
> 2) Use QR 200F plenum sprinklers and avoid locating them directly above
> the gaps.
>
> I modelled a piece of your scenario - - (4) panels with (3) gaps 'left to
> right' at 3.5m height, and a continuous structural ceiling at 4m.
> On the floor below the far left gap I put a 1,700 kW/m^2, t^2, FAST fire.
> The panels are 1.1m wide and the gaps are .05m wide. Centered in the far
> right gap is a QR, 155F, with a bulb height of 3.475m. Between 0 and 3m
> height I used .05m^3 grid cells, and between 3 and 4m I used .025m^3.
> Activation time was 99 sec. (14 hour calc time).
> Then I eliminated the gaps and ran it that way.
> Activation time was 94 sec.
>
> This would be an ideal scenario to model in detail using the Cloud Ceiling
> Study you mentioned as the template. In fact you can copy/paste the sample
> input file at the end of the report (from pdf to notepad), 'fix' a couple
> things that get lost in that translation, and start tweeking to your
> physical dimensions. Your clouds are not flat, but they are coplanar, and
> the plenum depth is consistent.
>
> wbr,
>
> Brad Casterline
>
> On May 29, 2016 3:48 PM, "Nicky Marshall" <[email protected]>
> wrote:
>
> 10 bays formed with Laminated timber beams, each with 24 panels.
>
>
>
> *Nicky Marshall*
>
> *Southern Regional Manager*
>
> *PROTECH DESIGN LIMITED*
>
> *Specialist Fire Protection Consultants*
>
> *Phone: *+64 (0)3 579 5577  *Mobile: *+64 (0)21 433 488  *Email:*
> [email protected]  *Skype: *nicky-marshall *Web:*
> www.protechdesign.co.nz
>
> *Address:*105A Alabama Rd, Redwoodtown, Blenheim 7201, NZ *Postal: *PO
> Box 4022, Redwood Village, Blenheim 7242, NZ
>
>
>
> *From:* Matthew J Willis [mailto:[email protected]]
> *Sent:* Saturday, 28 May 2016 1:33 AM
> *To:* [email protected]
> *Subject:* RE: Cloud ceilings & sprinklers in gaps
>
>
>
> How many clouds?
>
> I ask because technically sprinklers are not required under them. You
> stated 3’-6”..
>
>
>
> R/
>
> Matt
>
>
>
> *From:* Sprinklerforum [
> mailto:[email protected]
> <[email protected]>] *On Behalf Of *Nicky
> Marshall
> *Sent:* Thursday, May 26, 2016 10:30 PM
> *To:* [email protected]
> *Subject:* Cloud ceilings & sprinklers in gaps
>
>
>
> I would appreciate if anyone has some thoughts on this arrangement:
>
>
>
> ~4m (13ft) high roof, ~3.5m (11.5 ft) high ceiling.  Both slope 3 degrees.
>
> The ‘ceiling’ is to be made up of many Autex acoustic panels 1.1 x 2.3m
> (3.6 x 7.5 ft), non-combustible, suspended with 50mm (2 in) gaps around
> them.
>
> There will be sprinklers in the roof space because there are cable trays
> with loads of combustible cables.
>
> They architect wants to put the sprinklers in the 50mm gaps to avoid
> cutting holes in the acoustic panels.
>
>
>
> Whilst we are designing to NZS 4541, this code is silent on cloud ceilings
> or anything like this, so I am looking for guidance from other sources.
>
> I note NFPA 13:2016 clause 8.15.24 gives some guidance and it seems to
> indicate our ceiling arrangement would not require sprinklers above the
> clouds or have any specific sprinkler location requirements.
>
> I am also aware of the Fire Protection Research Foundation report on cloud
> ceilings.  This seemed to suggest that each cloud must have its own
> sprinkler – but doesn’t test with such small gaps – and recommends further
> study in this area where coverage can be achieved without sprinklers in
> every cloud.
>
>
>
> Three questions:
>
> Are the gaps small enough to just call this a ceiling – not a cloud
> ceiling (what size gap affects the plume flow enough to make a difference)?
>
> Is it acceptable to locate the sprinklers within the small gaps, or will
> this location significantly affect their operation?
>
> Do we have to cumulatively flow sprinklers above and below the ceiling, or
> since NFPA permits this arrangement to not have roof space sprinklers
> (suggesting heat flow into this space is not significant?), this would not
> be required?
>
>
>
> Kind regards
>
>
>
> *Nicky Marshall*
>
> *Southern Regional Manager*
>
> *PROTECH DESIGN LIMITED*
>
> *Specialist Fire Protection Consultants*
>
> *Phone: *+64 (0)3 579 5577  *Mobile: *+64 (0)21 433 488  *Email:*
> [email protected]  *Skype: *nicky-marshall *Web:*
> www.protechdesign.co.nz
>
> *Address:*105A Alabama Rd, Redwoodtown, Blenheim 7201, NZ *Postal: *PO
> Box 4022, Redwood Village, Blenheim 7242, New Zealand
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to