All that is required is "restraint".  That can be 12 ga. wire if you so
choose.  Look at NFPA 13, 2013 ed., 9.2.3.7 & the Annex material for it.
The same criteria goes back two or three editions.

 

Thank you,

 

Bob Knight, CET III

208-318-3057

 

  _____  

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Taylor Schumacher
Sent: Thursday, June 09, 2016 1:57 PM
To: [email protected]
Subject: Lateral support for sprigs

 

I have an AHJ in Iowa (non-seismic) looking for a listing for lateral
supports on sprigs in an attic. We have sprigs for back to back attic
sprinklers running from the main to the peak of the roof and have them
supported with loop hanger ring-rod-and threaded fastener.

 

I cannot find anything that requires a listing for this assembly nor can I
find any listing for something like this.

 

Any help would be appreciated.

 

TAYLOR SCHUMACHER

Security Fire Sprinkler 

P  320.656.0847  |  F  320.656.0312  |  E  [email protected]

 