The best way to address it is to take the AHJ to the sections in 13 that
call out restraint.  With a smile, explain that there are no listed
restraints for this application because the purpose is to prevent lateral
movement but not to supply bracing.  Per the standard restraint is a "lesser
degree" and that standard hanger materials may be used as one of several
options including the use of 12 ga. wire.  Since you have used one of the
options it should become self explanatory.

 

Thank you,

 

Bob Knight, CET III

208-318-3057

 

  _____  

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Taylor Schumacher
Sent: Thursday, June 09, 2016 3:59 PM
To: [email protected]; [email protected]
Subject: RE: Lateral support for sprigs

 

That's exactly how I interpreted it. That assembly prevents the pipe from
moving at the grooved coupling on the main as is required to keep the head
within the design criteria.

 

Just have never been questioned on it and am wondering if anyone else has.
And if so, what is the best solution.

 

TAYLOR SCHUMACHER

Security Fire Sprinkler 

P  320.656.0847  |  F  320.656.0312  |  E  [email protected]

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Bob
Sent: Thursday, June 09, 2016 3:45 PM
To: [email protected]
Subject: RE: Lateral support for sprigs

 

All that is required is "restraint".  That can be 12 ga. wire if you so
choose.  Look at NFPA 13, 2013 ed., 9.2.3.7 & the Annex material for it.
The same criteria goes back two or three editions.

 

Thank you,

 

Bob Knight, CET III

208-318-3057

 

  _____  

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Taylor Schumacher
Sent: Thursday, June 09, 2016 1:57 PM
To: [email protected]
Subject: Lateral support for sprigs

 

I have an AHJ in Iowa (non-seismic) looking for a listing for lateral
supports on sprigs in an attic. We have sprigs for back to back attic
sprinklers running from the main to the peak of the roof and have them
supported with loop hanger ring-rod-and threaded fastener.

 

I cannot find anything that requires a listing for this assembly nor can I
find any listing for something like this.

 

Any help would be appreciated.

 