Don't water curtains require a deluge approach. I'm not sure what that
configuration shown in 13 is supposed to do but certainly not a full curtain
around the opening.

On Monday, June 13, 2016, Tim Stone <[email protected]> wrote:

> Matt,
>
>
>
> My take and past practice is to use pendent heads as shown in figure
> A.8.15.4. The idea and I believe intent for the water to spray on the Draft
> Stop and fall down to the floor thus forming the “Water Curtain”. If you
> were to use Sidewalls I would think they need to point at the Draft Stop to
> perform that function. Chapter 8.15.4 Vertical Openings, 2010 ed.
>
>
>
> Regards,
>
> *G. Tim Stone*
>
>
>
> *G. Tim Stone Consulting, LLC*
>
> *NICET Level III Engineering Technician*
>
> *Fire Protection Sprinkler Design*
>
> *and Consulting Services*
>
>
>
> *                117 Old Stage Rd. - Essex Jct., VT. 05452*
>
> *CELL: (802) 373-0638   TEL: (802) 434-2968   Fax: (802) 434-4343*
>
>                            [email protected]
> <javascript:_e(%7B%7D,'cvml','[email protected]');>
>
>
>
> *From:* Sprinklerforum [mailto:
> [email protected]
> <javascript:_e(%7B%7D,'cvml','[email protected]');>]
> *On Behalf Of *Matt Grise
> *Sent:* Monday, June 13, 2016 12:53 PM
> *To:* [email protected]
> <javascript:_e(%7B%7D,'cvml','[email protected]');>
> *Subject:* RE: Closely spaced heads at vertical opening
>
>
>
> These would be mounted in the draftstop (a boxed out steel I-beam) pointed
> away from the opening.
>
>
>
> I am not clear on the intent of the design. The closely spaced sidewall
> sprinklers would cover more floor space than closely spaced uprights or
> pendants – but they would not throw as much water against the draft stop.
> Not sure how it would compare in terms of effectiveness.
>
>
>
> Matt Grisé PE*, LEED AP, NICET II
> Sales Engineer
> *Alliance Fire Protection*
>
> 130 w 9th Ave.
> North Kansas City, MO 64116
>
>
> **Licensed in KS & MO*
>
>
>
> 913.888.0647 ph
> 913.888.0618 f
> 913.526.7443 cell
> *www. AFPsprink.com*
>
>
>
>
>
> *From:* Sprinklerforum [
> mailto:[email protected]
> <javascript:_e(%7B%7D,'cvml','[email protected]');>]
> *On Behalf Of *Michael Hill
> *Sent:* Monday, June 13, 2016 11:37 AM
> *To:* <[email protected]
> <javascript:_e(%7B%7D,'cvml','[email protected]');>>
> *Subject:* Re: Closely spaced heads at vertical opening
>
>
>
> Sidewalks pointed at the draft stop?
>
> I thought part of the reasoning was to have water hit the draft stop and
> create a wall of water.
>
>
>
> Mike Hill
>
> Sent from my iPhone
>
>
> On Jun 13, 2016, at 12:18 PM, Matt Grise <[email protected]
> <javascript:_e(%7B%7D,'cvml','[email protected]');>> wrote:
>
> I have an application where an open stairway will require closely spaced
> heads and draft stopping. The construction of the opening lends itself to
> the use of sidewall sprinklers set in the draftstop to serve as the closely
> spaced heads. Is there anything that prohibits this? In reviewing the
> handbook, it only mentions sprinklers – not a particular type, but this
> still seems ‘out of the ordinary’.
>
>
>
> Thoughts?
>
>
>
> Thanks!
>
>
>
> Matt Grisé PE*, LEED AP, NICET II
> Sales Engineer
> *Alliance Fire Protection*
>
> 130 w 9th Ave.
> North Kansas City, MO 64116
>
>
> **Licensed in KS & MO*
>
>
>
> 913.888.0647 ph
> 913.888.0618 f
> 913.526.7443 cell
> *www. AFPsprink.com <http://AFPsprink.com>*
>
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> <javascript:_e(%7B%7D,'cvml','[email protected]');>
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>

-- 
Sent from Gmail Mobile
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to