Matt,

 

Chapter 11.3.3 “Water Curtain” design

 

Deluge not required.

 

Regards,

G. Tim Stone

 

G. Tim Stone Consulting, LLC

NICET Level III Engineering Technician

Fire Protection Sprinkler Design

and Consulting Services

 

                117 Old Stage Rd. - Essex Jct., VT. 05452

CELL: (802) 373-0638   TEL: (802) 434-2968   Fax: (802) 434-4343

                           [email protected] <mailto:[email protected]> 

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of rongreenman
Sent: Monday, June 13, 2016 2:36 PM
To: [email protected]
Subject: Re: Closely spaced heads at vertical opening

 

Don't water curtains require a deluge approach. I'm not sure what that 
configuration shown in 13 is supposed to do but certainly not a full curtain 
around the opening. 

On Monday, June 13, 2016, Tim Stone <[email protected] 
<mailto:[email protected]> > wrote:

Matt,

 

My take and past practice is to use pendent heads as shown in figure A.8.15.4. 
The idea and I believe intent for the water to spray on the Draft Stop and fall 
down to the floor thus forming the “Water Curtain”. If you were to use 
Sidewalls I would think they need to point at the Draft Stop to perform that 
function. Chapter 8.15.4 Vertical Openings, 2010 ed.

 

Regards,

G. Tim Stone

 

G. Tim Stone Consulting, LLC

NICET Level III Engineering Technician

Fire Protection Sprinkler Design

and Consulting Services

 

                117 Old Stage Rd. - Essex Jct., VT. 05452

CELL: (802) 373-0638   TEL: (802) 434-2968   Fax: (802) 434-4343

                           [email protected] 
<javascript:_e(%7B%7D,'cvml','[email protected]');> 

 

From: Sprinklerforum [mailto:[email protected] 
<javascript:_e(%7B%7D,'cvml','[email protected]');>
 ] On Behalf Of Matt Grise
Sent: Monday, June 13, 2016 12:53 PM
To: [email protected] 
<javascript:_e(%7B%7D,'cvml','[email protected]');> 
Subject: RE: Closely spaced heads at vertical opening

 

These would be mounted in the draftstop (a boxed out steel I-beam) pointed away 
from the opening.

 

I am not clear on the intent of the design. The closely spaced sidewall 
sprinklers would cover more floor space than closely spaced uprights or 
pendants – but they would not throw as much water against the draft stop. Not 
sure how it would compare in terms of effectiveness.

 

Matt Grisé PE*, LEED AP, NICET II  
Sales Engineer 
Alliance Fire Protection 

130 w 9th Ave.
North Kansas City, MO 64116


*Licensed in KS & MO 

 

913.888.0647 ph 
913.888.0618 f 
913.526.7443 cell 
www. AFPsprink.com 

 

 

From: Sprinklerforum [mailto:[email protected] 
<javascript:_e(%7B%7D,'cvml','[email protected]');>
 ] On Behalf Of Michael Hill
Sent: Monday, June 13, 2016 11:37 AM
To: <[email protected] 
<javascript:_e(%7B%7D,'cvml','[email protected]');> >
Subject: Re: Closely spaced heads at vertical opening

 

Sidewalks pointed at the draft stop?

I thought part of the reasoning was to have water hit the draft stop and create 
a wall of water.

 

Mike Hill

Sent from my iPhone


On Jun 13, 2016, at 12:18 PM, Matt Grise <[email protected] 
<javascript:_e(%7B%7D,'cvml','[email protected]');> > wrote:

I have an application where an open stairway will require closely spaced heads 
and draft stopping. The construction of the opening lends itself to the use of 
sidewall sprinklers set in the draftstop to serve as the closely spaced heads. 
Is there anything that prohibits this? In reviewing the handbook, it only 
mentions sprinklers – not a particular type, but this still seems ‘out of the 
ordinary’.

 

Thoughts?

 

Thanks!

 

Matt Grisé PE*, LEED AP, NICET II  
Sales Engineer 
Alliance Fire Protection 

130 w 9th Ave.
North Kansas City, MO 64116


*Licensed in KS & MO 

 

913.888.0647 ph 
913.888.0618 f 
913.526.7443 cell 
www. AFPsprink.com <http://AFPsprink.com>  

 

 

_______________________________________________
Sprinklerforum mailing list
[email protected] 
<javascript:_e(%7B%7D,'cvml','[email protected]');> 