Jay,

 

If you can’t use the reduction for QR sprinklers, calculate both scenarios you 
described and use the most demanding one for your submittal or better yet, show 
both areas on your drawings and then there is no question from the AHJ.

 

You can omit the sprinklers in the small compartments from the 1500 sf remote 
area but not the sprinklers in the corridor.

 

Cliff

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Jay Stough
Sent: Wednesday, July 13, 2016 10:51 AM
To: Sprinkler Forum <[email protected]>
Subject: Calculating extended coverage

 

I have a nursing care facility that I am trying to calc.  Must be 13 (2007) 
light.  Can not use room design or residential method per state AHJ.  The 
building is shaped like an upper case H with the bottom legs cut off.  There 
are 4 rooms on one side of the corridor and 3 rooms on the other side of the 
corridor in each upper leg that use extended coverage sprinkler in each room.  
Also 1 standard spray sprinkler in a closet and one standard spray sprinkler in 
a bathroom in each room.  Sprinklers in the corridor are standard spray also.  
Since I am using extended coverage sprinklers, I need to calculate 5 minimum.  
The sprinklers cover 16'3 X 14', so need to calc at the 18' X 18' rate.  
22.4.6.2 allows me in "rooms like closets, washrooms and similar small 
compartments requiring only one sprinkler shall be permitted to be omitted from 
calculations within the area of application".   Can I calculate 6 extended 
coverage sprinklers, without the corridor or "small rooms or compartments" for 
my 1500 sq ft?  Or should I calc 5 extended coverage and the hallway sprinklers 
in the 1500 sq ft?  