Use the small room rule where the head is allowed to be 9' from one wall and 
calc as if it were a 16 x 16. Less pressure and water overages. 4 head calc for 
900 sqft.

"For I am not ashamed of the gospel, because it is God's power for salvation to 
everyone who believes..." HCS Romans 1:16 
"Therefore having overlooked the times of ignorance, God is now declaring to 
men that all people everywhere should repent,..." NASB Acts 17:30

> On Jul 13, 2016, at 9:50 AM, Jay Stough <[email protected]> wrote:
> 
> I have a nursing care facility that I am trying to calc.  Must be 13 (2007) 
> light.  Can not use room design or residential method per state AHJ.  The 
> building is shaped like an upper case H with the bottom legs cut off.  There 
> are 4 rooms on one side of the corridor and 3 rooms on the other side of the 
> corridor in each upper leg that use extended coverage sprinkler in each room. 
>  Also 1 standard spray sprinkler in a closet and one standard spray sprinkler 
> in a bathroom in each room.  Sprinklers in the corridor are standard spray 
> also.  Since I am using extended coverage sprinklers, I need to calculate 5 
> minimum.  The sprinklers cover 16'3 X 14', so need to calc at the 18' X 18' 
> rate.  22.4.6.2 allows me in "rooms like closets, washrooms and similar small 
> compartments requiring only one sprinkler shall be permitted to be omitted 
> from calculations within the area of application".   Can I calculate 6 
> extended coverage sprinklers, without the corridor or "small rooms or 
> compartments" for my 1500 sq ft?  Or should I calc 5 extended coverage and 
> the hallway sprinklers in the 1500 sq ft?  
> 
> Jay Stough 
> NICET IV LAYOUT 
> NICET III ITM
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org