Evan at 900 sq ft, you still need to get 5 sprinklers.

You may be able to use 2.8k or 4.2k sprinklers in the closets and bathrooms. That way, the 900 sq ft may not be too bad.

I would just throw on several remote areas and see what one is the most demanding. Do 5 ex cov sprinklers as you originally stated.

22.4.6.2 says you can eliminate those sprinklers in small rooms if you do 1500 sq ft.

You just have several different options. See which one is the most demanding.

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]

http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign
LinkedIn: https://www.linkedin.com/in/travismack

On 7/13/2016 8:14 AM, Art Tiroly wrote:

What state are you in?

Can I assume you are planning quick response sprinklers.

Then why not 900 SF area of application allowance?

What part of the code is AHJ using for this requirement.

There are residential rules in 13.

Use residential heads with .10 density

Art Tiroly

Tiroly and Associates

*From:*Sprinklerforum [mailto:[email protected]] *On Behalf Of *Jay Stough
*Sent:* Wednesday, July 13, 2016 10:51 AM
*To:* Sprinkler Forum <[email protected]>
*Subject:* Calculating extended coverage

I have a nursing care facility that I am trying to calc. Must be 13 (2007) light. Can not use room design or residential method per state AHJ. The building is shaped like an upper case H with the bottom legs cut off. There are 4 rooms on one side of the corridor and 3 rooms on the other side of the corridor in each upper leg that use extended coverage sprinkler in each room. Also 1 standard spray sprinkler in a closet and one standard spray sprinkler in a bathroom in each room. Sprinklers in the corridor are standard spray also. Since I am using extended coverage sprinklers, I need to calculate 5 minimum. The sprinklers cover 16'3 X 14', so need to calc at the 18' X 18' rate. 22.4.6.2 allows me in "rooms like closets, washrooms and similar small compartments requiring only one sprinkler shall be permitted to be omitted from calculations within the area of application". Can I calculate 6 extended coverage sprinklers, without the corridor or "small rooms or compartments" for my 1500 sq ft? Or should I calc 5 extended coverage and the hallway sprinklers in the 1500 sq ft?

/Jay Stough/

NICET IV LAYOUT

NICET III ITM



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to