I would think that the obstruction rules of NFPA 13 Ch 8 would apply to the 
ESFR (i.e. 36" clear below deflector) regardless of the hazard. ESFR's were 
developed and listed by U.L. with additional room below the head to allow for 
the "Discharge Umbrella" to develop.
Just my opinion... John W. Farabee, 

    On Wednesday, August 31, 2016 1:37 PM, Gregg Fontes <[email protected]> 
wrote:
 

  <!--#yiv0122441544 _filtered #yiv0122441544 {font-family:"Cambria 
Math";panose-1:2 4 5 3 5 4 6 3 2 4;} _filtered #yiv0122441544 
{font-family:Calibri;panose-1:2 15 5 2 2 2 4 3 2 4;}#yiv0122441544 
#yiv0122441544 p.yiv0122441544MsoNormal, #yiv0122441544 
li.yiv0122441544MsoNormal, #yiv0122441544 div.yiv0122441544MsoNormal 
{margin:0in;margin-bottom:.0001pt;font-size:12.0pt;font-family:"Times New 
Roman", serif;}#yiv0122441544 a:link, #yiv0122441544 
span.yiv0122441544MsoHyperlink 
{color:blue;text-decoration:underline;}#yiv0122441544 a:visited, #yiv0122441544 
span.yiv0122441544MsoHyperlinkFollowed 
{color:purple;text-decoration:underline;}#yiv0122441544 
span.yiv0122441544apple-style-span {}#yiv0122441544 
span.yiv0122441544EmailStyle18 {font-family:"Times New Roman", 
serif;color:black;font-weight:normal;font-style:normal;text-decoration:none 
none;}#yiv0122441544 .yiv0122441544MsoChpDefault {font-size:10.0pt;} _filtered 
#yiv0122441544 {margin:1.0in 1.0in 1.0in 1.0in;}#yiv0122441544 
div.yiv0122441544WordSection1 {}-->2016 NFPA 13 – 8.4.6.6 Occupancy and Hazard. 
 (Handbook)  In an existing warehouse building being converted to a non-storage 
use, the existing ESFR sprinklers can remain in place provided the new use is 
either light or ordinary hazard.  My questions is if it is ordinary hazard 
occupancy, do the ESFR obstruction rule apply or due the obstruction rules for 
standard systems apply (i.e. conventional)?  As an example, would 30” x 48” 
lights be allowed to hang below the ESFR sprinkler and not be considered an 
obstruction?   Same with new duct work greater than 24”? Etc.

 Thanks, Gregg Fontes Cen-Cal Fire Systems, Inc. 209-334-9119    
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


   
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to