Especially since Chapter 8 and rules are divided by the Sprinkler Type, not 
hazard.

R/
Matt

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of 321
Sent: Wednesday, August 31, 2016 12:14 PM
To: [email protected]
Subject: Re: ESFR - Ordinary Hazard

I would think that the obstruction rules of NFPA 13 Ch 8 would apply to the 
ESFR (i.e. 36" clear below deflector) regardless of the hazard. ESFR's were 
developed and listed by U.L. with additional room below the head to allow for 
the "Discharge Umbrella" to develop.

Just my opinion...

John W. Farabee,

On Wednesday, August 31, 2016 1:37 PM, Gregg Fontes 
<[email protected]<mailto:[email protected]>> wrote:

2016 NFPA 13 – 8.4.6.6 Occupancy and Hazard.  (Handbook)  In an existing 
warehouse building being converted to a non-storage use, the existing ESFR 
sprinklers can remain in place provided the new use is either light or ordinary 
hazard.  My questions is if it is ordinary hazard occupancy, do the ESFR 
obstruction rule apply or due the obstruction rules for standard systems apply 
(i.e. conventional)?  As an example, would 30” x 48” lights be allowed to hang 
below the ESFR sprinkler and not be considered an obstruction?   Same with new 
duct work greater than 24”? Etc.
Thanks,
Gregg Fontes
Cen-Cal Fire Systems, Inc.
209-334-9119


_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to