I think duration of supply is the biggest concearn.
If two tanks shoot their w*d in 5 minutes, it would take twelve tanks to
last 30 minutes.
On Sep 18, 2016 6:20 PM, "Scott Futrell" <sco...@ffcdi.com> wrote:

> Scot,
>
>
>
> The simple answer is yes.  The area and construction and other exemptions
> are not allowed if rooms/areas that are required to be sprinklered for
> fully sprinklered buildings are not.
>
>
>
> Scott
>
>
>
> Office: (763) 425-1001 x 2
>
> Cell: (612) 759-5556
>
>
>
> *From:* Sprinklerforum [mailto:sprinklerforum-bounces@lists.firesprinkler.
> org] *On Behalf Of *å... ....
> *Sent:* Friday, September 16, 2016 2:16 PM
> *To:* sprinklerforum@lists.firesprinkler.org
> *Subject:* Do gas-suppression systems in electrical rooms (for example)
> w/o sprinklers void the exemptions awarded to a fully-sprinklered occupancy?
>
>
>
>
>
>
> My guess as to the answer of this is, "yes",   but I want to be sure.
>
> Feel comfortable to offer your judgment.
>
>
>
> If a design guide calls for the occupancy to be sprinklered throughout,
> then if electronics and electrical rooms are not sprinklered but protected
> with alternative gas suppression systems, are the lucrative exemptions
> awarded when a building is "sprinklered throughout", withheld?
>
>
>
> I sense this is a building code question, not an NFPA 13 question.
>
>
>
>
>
> Commentary to 2009 IBC -903.1.1 states in its last sentence, if sprinklers
> are not installed as backup for alternative (i.e. gas systems ), then the
> lucrative exemptions granted via reduction to other fire safety systems
> throughout this building code are not awarded due to the lower safety
> offered by the less reliable gas suppression systems.
>
>
>
>
>
> 2009 NFPA 101 -9.7.3 commentary says it is a good idea to have sprinklers
> as backup to the 'special' first-line-of-defense alternative systems, but
> it does not go so far, as far as I could tell, as to eliminate the
> financially beneficial trade-offs linked to an occupany/building that is
> sprinklered throughout, in the event that electronic/electrical rooms have
> only gas-suppression without automatic sprinklers.
>
>
>
> Section -19.3.5.4 of 2009 NFPA 101 says sprinklers should be throughout a
> health care facility, but in the instance where the AHJ allows omission,
> then section -19.3.5.5 states these areas need by Type I or II construction
> and enclosed with FRR.    But the commentary to the NFPA 101 on these
> section says the lucrative sprinkler exemptions remain valid.
>
>
>
> The IBC is clear: sprinklers throughout.
>
> The NFPA 101 seems clear—except for health care.
>
> I do not know what the 2009 NFPA 5000 states.
>
>
>
> If there are electronic/electrical rooms without sprinklers, but with
> alternative gas agent suppression, are the exceptions for '*fully-sprinklered
> building*' withheld? I think – yes. The US Air Force seems to agree with
> this suggestion.
>
>
>
> Segueing into WHY using only-gaseous agent fire suppression is NOT enough,
> consider the Air Force wording, already 15 years old, by the time of first
> draft.  ETL 01-18 is paraphrased below:
>
>
>
> the US Air [1] states that sprinklers will be provided as backup to
> “clean” agent systems because the sprinklers are THAT reliable.  If any
> customer has a big and quasi reliable database, I would argue the US Air
> Force would be in that group.  The US Air Force requires fire sprinklers
> over mission critical electrical gear. The US Air Force discourages
> pre-action sprinkler systems to wet pipe systems, which again is in
> concurrence with the experiences and stories I have encountered.   The US
> Air Force states “Leaky roofing, air conditioning, and plumbing systems
> present a far greater risk of water damage than a wet-pipe sprinkler system
> properly installed in accordance with NFPA 13.
>
> Further, mission essential information technology rooms shall be located
> only in facilities that are fully sprinklered, by a wet-pipe sprinkler
> system[2]. Alternative suppression system to wet-pipe standard spray
> sprinkler are allowed on approval of Major Command, but the alternatives
> both involve--water suppression: water mist and water pre-action.
> Pre-action systems are of significantly lower reliability than wet-pipe
> systems.   [3].
>
>
>
> [1]. ETL 01-18, Engineering Technical Letter (ETL 01-18) Fire Protection
> Criteria – Electronic Equipment Installations 24 Oct 2001, (pp. -7.3.10.2
> last sentence
>
> [2].  op. cit.,  ETL 01-18, -7.3.9.1
>
> [3]. op. cit.,  Ibid, -7.3.10.2
>
>
>
> Scot Deal
>
> Excelsior Risk/Fire Engineering
>
> gms:  +420 722 141 478  GMT+1
>
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
>