And how do you demonstrate equivalency?

On Thu, Sep 22, 2016 at 2:45 AM, å... .... <eurekaig...@gmail.com> wrote:

>
>
>
> This is a follow up.  It regards the prescriptions of NFPA 5000 on use of
> alternative suppression systems to sprinklers...and this impact on
> exemption from construction features.
>
> 2006 NFPA 5000  -55.5.3   Construction alternatives for automatic
> sprinkler systems shall not be permitted *for those portions* of
> buildings protected by alternative extinguishing systems, unless
> equivalency is demonstrated.
>
> The NFPA 5000 is notably more liberal on this issue than the IBC.  Sure,
> IBC allows the demonstration of equivalency between an alternative
> extinguishing system and sprinklers, but 2006 IBC -903.1.1 does not remind
> and thus gently suggest this feature to the reader.  Further,  IBC seems to
> extend the forfeiture-of-construction-alternatives throughout the
> occupancy/building,  rather than the NFPA 5000 limiting forfeiture to only
> those portions of the building where the alternative extinguishing agents
> are located.
>
> Scot Deal
> Excelsior Risk/Fire Engineering
> gsm:  +420 722 141 478  GMT + 1
>
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
>


-- 
Ron Greenman

4110 Olson Dr., NW
Gig Harbor, WA 98335

rongreen...@gmail.com

253.576.9700

The Universe is monstrously indifferent to the presence of man. -Werner
Herzog, screenwriter, film director, author, actor and opera
director (1942-)
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to