I have had to do this on some 13R group homes. The AHJ wouldn't accept a single
2-1/2. Seems like overkill. Two 2-1/2" connections fed from a 1500 gpm pump for
a 55 gpm demand. We ran 4" to the riser room and connected with a 4 x 1-1/4
welded outlet.