And if you were dealing with a 5.6K sprinkler installed in a mech tee would you 
need to use ½” pipe for the equivalent length (for the difference between a 
standard tee and the mechanical tee manufacturer’s equivalent loss)?

 

Regards.

 

Damien Shannon.

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Brad Casterline
Sent: 29 October 2016 17:24
To: [email protected]
Subject: Re: Hydraulic losses when using a Mechanical Tee on Sprinkler Outlet

 

This is actually pretty dramatic Ron. In Russell's case, if the K25 head is in 
a 1" welded pipe-o-let the pressure required at the branch line is the same as 
at the head, where as if it is in a 1" mechanical tee the pressure required at 
the branch line is the same as if the head was on a 1" x 11'-0" sprig or drop!

Of course if the K for a K25 was established when it was in a 1" mech tee, it 
could rightly be excluded. 

Both welded outlets and mech tees have similar hole sizes, but I think the 
gaskets on mech tees reduce the AREA of the hole, which plays the biggest part 
of the ultimate Coefficient of Discharge, aka, K-Factor.

Just my two no nonsense :)

Brad

On Oct 29, 2016 11:02 AM, "rongreenman ." <[email protected] 
<mailto:[email protected]> > wrote:

Are we once again worrying about the difference between 0.003 psi and 0.004 psi?

 

 If I recall the number we're trying to compare demand against supply is based 
on a formulae with a constant (average), an average C-factor of deterioration 
based on variable conditions over many years, a nominal diameter, and a 
velocity pressure determined by holding a pitot in a stream of water that's 
trying to rip the pitot out of your had while you take an average reading from 
a bouncing gauge that has a +/– built in. Then we do the math, round to the 
nearest 50 gpm, and apply it to a graph so small that the width of the line has 
an effect. 

 

And as Brad said the fitting is calculated into the K factor of the sprinkler. 
And as someone else noted the flexible drop is a drop, not a fitting. It has a 
fitting the sprinkler screws into. It also has a friction loss value that has 
to be an average as it doesn't take the curves into account. And do we 
calculate the gain from the elevation change?

 

On Fri, Oct 28, 2016 at 8:33 AM, Brad Casterline <[email protected] 
<mailto:[email protected]> > wrote:

Here is my original reply, for what it's worth...

 

 

Russell,

 

My understanding is we do not have to figure the loss for the fitting the

sprinkler is in because when the K Factor was being established it was in a

fitting.

NFPA 13 (2016) 23.4.4.8.1 (9) confirms that.

But it's a good question because we're supposed to use a manufacturer's

published loss if they have one.

So would it make sense to, if the published loss is greater, subtract the

loss shown in 13, and include that difference?

 

Brad

 

 


  _____  


From: Sprinklerforum [mailto:[email protected] 
<mailto:[email protected]> ] On Behalf Of Brad 
Casterline
Sent: Friday, October 28, 2016 10:19 AM
To: [email protected] 
<mailto:[email protected]> 
Subject: RE: Hydraulic losses when using a Mechanical Tee on Sprinkler Outlet

 

Here is the e-mail I sent to our in-office guy whom submits questions to NFPA:

 

 

*****

"From NFPA 13- 2016

 

 

23.4.3.1.1 Table 23.4.3.1.1 shall be used to determine the

equivalent length of pipe for fittings and devices unless manufacturer’s

test data indicate that other factors are appropriate.

 

23.4.4.8.1

(9) Friction loss shall be excluded for the fitting directly

connected to a sprinkler.

 

 

A 1" tee in the table is 5' equivalent length.

A mechanical tee with 1" outlet is 11' equivalent length.

 

If the sprinkler is directly attached to the mechanical tee do we still exclude 
it?"

*****

 

 

When we got the recent response Gregory pasted, I asked the guy for the exact 
wording of the submitted question, but since submitting a question on-line 
'disappears' once submitted, it was not available. He said he reworded mine a 
little, but thinks the last line (which is what this is all about) was clear.

 

Personally, I like my original reply to Russell, but I'm just a Tech, so 
there's that :)

 

Brad 

 

 


  _____  


From: Sprinklerforum [mailto:[email protected] 
<mailto:[email protected]> ] On Behalf Of Russell 
& Carol Gregory
Sent: Thursday, October 27, 2016 10:01 PM
To: [email protected] 
<mailto:[email protected]> 
Subject: RE: Hydraulic losses when using a Mechanical Tee on Sprinkler Outlet

 

Ken, and others,

We have been excluding the loss for a welded outlet or a mech tee when a 
sprinkler is directly attached. If the outlet is to feed a pipe (regardless of 
length) then the standard loss for a branch on tee would be used, however if 
the Manufacturers Data Sheet states that the loss in a clamp tee is greater 
than the loss in Table 23.4.3.1.1 (NFPA 13 2016) for a side outlet of tee, THEN 
the ADDITIONAL LOSS shall be included. I think they should say the Higher EQL 
Loss should be used so you don’t use less than the Table Loss.

 

Here is a recent NFPA Response to a similar question;

 

Table 23.4.3.1.1 is required to be used to determine the equivalent length

of pipe for fittings and devices unless manufacturers' test data indicate

that other factors are appropriate. In your situation since the manufacturer

specifies an equivalent length of 11 feet, you are required to use 11 feet

for the equivalent length. 

 

In regards to Section 23.4.4.8(9) of the 2016 edition of NFPA 13, if an

extension is used with a tee, that tee must be included in the hydraulic

calculations. The allowance to use an extension is restricted to sprinklers

with a relative low discharge volume. They will most likely be used for

minor adjustments to interface with the ceiling.

 

This answers some of the other Forum responses to my questions but does not 
answer my problem. 

 

What I would like to see is a practical flow test done with a K36 (us k25) head 
and see if there is a significant difference between welded outlet, threaded 
tee and clamp tee. Does anyone know if this has been done???

 

Our AHJ has asked for the full loss to be included and this will nearly double 
the pressure required at a K-36 sprinkler from 345kPa(50psi) to around 
600kPa(90psi), if clamp tees are used. There is quite a variation between 
Brands for the stated EQL.

Makes life difficult if site staff change from welded to mechanical fittings 
and then buy a variety of brands!!!!!

 

Thanks for the responses.

Russell Gregory

 

 

From: Sprinklerforum [mailto:[email protected] 
<mailto:[email protected]> ] On Behalf Of Parsley 
Consulting
Sent: Friday, 28 October 2016 3:56 AM
To: [email protected] 
<mailto:[email protected]> 
Subject: Re: Hydraulic losses when using a Mechanical Tee on Sprinkler Outlet

 

Russell,
    Mark and Todd are both correct.  
    If the sprinkler is directly attached to the fitting, in this case the 
welded outlet or mechanical tee, the friction loss through that fitting is 
excluded from the hydraulic calculations, per NFPA 13, 23.4.4.7.1(9).  I don't 
know that I've ever had a set of calculations sent back with a comment that I 
didn't include the friction loss equivalent for the welded outlet or mechanical 
tee which was directly attached to the sprinkler.  
    Todd's comment is valid as well, however it's worth noting, I believe, that 
when you're designing a system with flexible drops you must account for the 
equivalent length of the device, using the manufacturer's data.  My own 
experience has been that those values are substantial.
sincerely,

Ken Wagoner, SET
Parsley Consulting
350 West 9th Avenue, Suite 206
Escondido, California 92025
Phone 760-745-6181 <tel:760-745-6181> 
Visit our website <http://www.parsleyconsulting.com/>  

On 10/27/2016 1:30 AM, Russell & Carol Gregory wrote:

I posted a message on this subject early this month but only received one 
reply(thanks Brad). This was surprising as I thought it was a serious problem 
if the full EQL for tee had to be added to calculations. Especially if the 
change was made on-site after design had been completed with welded outlets.

So my query is as follows;

 

When calculating a Range Pipe with welded threaded outlets for sprinklers it is 
not necessary to include a loss for the water leaving the range pipe and 
entering the sprinkler. The total pressure is assumed to apply to the sprinkler 
orfice.

This means that a 80nb pipe with a 25nb outlet and a k36 sprinkler does not 
have an additional loss added for the outlet fitting.

 

If I change my design and fabricate the 80nb range pipe with 80 x 25 Mechanical 
Tees for the Sprinkler outlet do I have to apply an additional loss factor for 
that fitting? The published EQL for Mech tees varies greatly between brands,( 
0.8m up to 2.4m). This means a head pressure of 345kPa would need around 600kPa 
in the range if this additional loss is added.

 

Questions;

1.       Is it common practice in USA to use 80 x 25 clamp/mechanical tees  for 
attaching large bore Storage Sprinklers directly to 80nb range pipes?

2.       Is it common practice to add in an additional loss for the clamp tee, 
in the hydraulic calculation, where the sprinkler is directly fitted to the tee 
outlet?  

 

I would appreciate the Forum members advise as to what is the standard practice 
in the USA.

 

Russell Gregory

Christchurch 

New Zealand

 

e-mail [email protected] <mailto:[email protected]> 

 

 

_______________________________________________
Sprinklerforum mailing list
[email protected] 
<mailto:[email protected]> 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

 


_______________________________________________
Sprinklerforum mailing list
[email protected] 
<mailto:[email protected]> 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org





 

-- 

Ron Greenman


4110 Olson Dr., NW
Gig Harbor, WA 98335

[email protected] <mailto:[email protected]> 

253.576.9700 <tel:253.576.9700> 

 

The Universe is monstrously indifferent to the presence of man. -Werner Herzog, 
screenwriter, film director, author, actor and opera director (1942-)


_______________________________________________
Sprinklerforum mailing list
[email protected] 
<mailto:[email protected]> 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to