I would say OPEN is to the temperature, not the bugs.  Also look at it from the 
potential to flash-over.  The screen will not hold in the heat.  Now have that 
discussion with the AHJ.

The TC member caveat - Not to be considered a formal interpretation of NFPA

Roland


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>