CHECK IBC. I THINK IT WILL REQUIRE THEM.

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Roland Huggins
Sent: November-07-16 11:10 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: 13D Porches

 

I would say OPEN is to the temperature, not the bugs.  Also look at it from
the potential to flash-over.  The screen will not hold in the heat.  Now
have that discussion with the AHJ.

 

The TC member caveat - Not to be considered a formal interpretation of NFPA

 

Roland

 

 

Roland Huggins, PE - VP Engineering

American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives

Dallas, TX

http://www.firesprinkler.org <http://www.firesprinkler.org/> 

 

 

 

On Nov 6, 2016, at 4:58 PM, Todd Williams <fpdcdes...@gmail.com> wrote:

 

 
<https://tr.cloudmagic.com/h/v6/emailtag/tag/1478480303/2d4c4b9cd9f303a04c4d
9c24d32f6571/ecdd64c309bb34b23eb65c654267bfff/4320b82257e7b25d61f3e788b5efb0
03/9efab2399c7c560b34de477b9aa0a465/ufo.gif> 

NFPA 13D allows for exclusion of sprinklers in open attached porches. Does
screening count as an enclosure?

Todd G Williams, PE

Fire Protection Design/Consulting

Stonington, CT

860-535-2080 (ofc)

860-608-4559 (cell)

 

via Newton Mail
<https://cloudmagic.com/k/d/mailapp?ct=ti&cv=9.2.5&pv=10.1.1&source=email_fo
oter_2> 

 

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

 

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to