What's the Seismic Design Category assigned by the Structural engineer for the project? A,B,C,D,E?
The Fire Protection Engineer should have clarified whether or not EQ bracing was required based on the above category which was determined by the structural EOR if it was done right or done at all. Craig L. Prahl Fire Protection Group Lead/SME CH2M 200 Verdae Blvd. Greenville, SC 29607 Direct - 864.920.7540 Fax - 864.920.7129 CH2MHILL Extension 77540 [email protected] From: Sprinklerforum [mailto:[email protected]] On Behalf Of Jerry Van Kolken Sent: Tuesday, December 06, 2016 5:06 PM To: [email protected] Subject: Seismic Requirements for Risk Category IV (Essential Facility) [EXTERNAL] I have a building being classified as an essential facility. I'm told that the building must be operation after an earthquake, whether or not that includes the sprinkler system, I will need to get RFI'd. But my question is would there be any special requirements for the hanging and bracing of the sprinkler system due this classification? Jerry Van Kolken Millennium Fire Protection Corp. 2950 San Luis Rey Rd. Oceanside, CA 92058 (760) 722-2722 FX 722-2730