What's the Seismic Design Category assigned by the Structural engineer for the 
project?  A,B,C,D,E?

The Fire Protection Engineer should have clarified whether or not EQ bracing 
was required based on the above category which was determined by the structural 
EOR if it was done right or done at all.


Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540
Fax - 864.920.7129
CH2MHILL Extension  77540
[email protected]


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Jerry Van Kolken
Sent: Tuesday, December 06, 2016 5:06 PM
To: [email protected]
Subject: Seismic Requirements for Risk Category IV (Essential Facility) 
[EXTERNAL]

I have a building being classified as an essential facility. I'm told that the 
building must be operation after an earthquake, whether or not that includes 
the sprinkler system,  I will need to get RFI'd. But my question is would there 
be any special requirements for the hanging and bracing of the sprinkler system 
due this classification?