Site class still doesn't tell much. You need the seismic design
category. But as far as I know, there is nothing about a risk category
that increases seismic requirements. It is set by the Seismic design
category and then calculations for your bracing loads.
Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]
http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign
LinkedIn: https://www.linkedin.com/in/travismack
On 12/7/2016 9:33 AM, Jerry Van Kolken wrote:
The site is Class C,
This project is in So. California, EQ bracing is always required. I
just wanted to know is there is anything special about Risk Category IV.
Jerry Van Kolken
/_Millennium Fire Protection_/
(760) 722-2722
*From:*Sprinklerforum
[mailto:[email protected]] *On Behalf Of
*[email protected]
*Sent:* Tuesday, December 06, 2016 2:16 PM
*To:* [email protected]
*Subject:* RE: Seismic Requirements for Risk Category IV (Essential
Facility)
What’s the Seismic Design Category assigned by the Structural engineer
for the project? A,B,C,D,E?
The Fire Protection Engineer should have clarified whether or not EQ
bracing was required based on the above category which was determined
by the structural EOR if it was done right or done at all.
*Craig L. Prahl**
*Fire Protection Group Lead/SME
*CH2M*
200 Verdae Blvd.
Greenville, SC 29607
Direct - 864.920.7540
Fax - 864.920.7129
CH2MHILL Extension 77540
[email protected] <mailto:[email protected]>
*From:* Sprinklerforum
[mailto:[email protected]] *On Behalf Of
*Jerry Van Kolken
*Sent:* Tuesday, December 06, 2016 5:06 PM
*To:* [email protected]
<mailto:[email protected]>
*Subject:* Seismic Requirements for Risk Category IV (Essential
Facility) [EXTERNAL]
I have a building being classified as an essential facility. I’m told
that the building must be operation after an earthquake, whether or
not that includes the sprinkler system, I will need to get RFI’d. But
my question is would there be any special requirements for the hanging
and bracing of the sprinkler system due this classification?
Jerry Van Kolken
/_Millennium Fire Protection Corp._/
2950 San Luis Rey Rd.
Oceanside, CA 92058
(760) 722-2722 FX 722-2730
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org