We have a grocery store that has a wavy kinda soffit (see dropbox file link 
below) around the perimeter of most of the store. The top of this soffit is 
approximately 5'0" below the overhead sprinklers & is less than 48" at the 
widest points. With that being said are additional heads needed in this lower 
soffit? In my opinion 8.6.5.2 would not apply since the pattern development is 
not affected so the next stop would be 8.6.5.3. The only thing that stands out 
to me there would be the 48" width we I do not have. So I say no additional 
heads needed below, what say you?