We have a grocery store that has a wavy kinda soffit (see dropbox file link below) around the perimeter of most of the store. The top of this soffit is approximately 5'0" below the overhead sprinklers & is less than 48" at the widest points. With that being said are additional heads needed in this lower soffit? In my opinion 8.6.5.2 would not apply since the pattern development is not affected so the next stop would be 8.6.5.3. The only thing that stands out to me there would be the 48" width we I do not have. So I say no additional heads needed below, what say you?
https://www.dropbox.com/s/3klcgh37fhowmp8/Wavy%20Soffit.pdf?dl=0 Brian Harris, CET BVS Systems Inc. Design Manager bvssystemsinc.com<http://bvssystemsinc.com/> Phone: 704.896.9989 Fax: 704.896.1935