Can you use the soffit against the wall rule from NFPA 13, 2013
8.6.5.1.2* Sprinklers shall be arranged to comply with one of the following 
arrangements:
(1) Subsection 8.5.5.2, Table 8.6.5.1.2, and Figure 8.6.5.1.2(a) shall be 
followed.
(2) Sprinklers shall be permitted to be spaced on opposite sides of 
obstructions not exceeding 4 ft (1.2 m) in width, provided the distance from 
the centerline of the obstruction to the sprinklers does not exceed one-half 
the allowable distance permitted between sprinklers.
(3) Obstructions located against the wall and that are not over 30 in. (762 mm) 
in width shall be permitted to be protected in accordance with Figure 
8.6.5.1.2(b).
(4) Obstructions located against the wall and that are not over 24 in. (610 mm) 
in width shall be permitted to be protected in accordance with Figure 
8.6.5.1.2(c). The maximum distance between the sprinkler and the wall
shall be measured from the sprinkler to the wall behind the obstruction and not 
to the face of the obstruction.
A.8.6.5.1.2 The intent of 8.6.5.1.2(3) is to apply to soffits that are located 
within the 18 in. (457 mm) plane from the sprinkler deflector. A soffit or 
other obstruction (i.e., shelf) located against a wall that is located entirely 
below the 18 in. (457 mm) plane from the sprinkler deflector should be in 
accordance with 8.6.5.3.3. (See Figure A.8.6.5.1.2.)

[cid:[email protected]]

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
[email protected]<mailto:[email protected]>

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of rongreenman .
Sent: Thursday, January 12, 2017 11:00 AM
To: [email protected]
Subject: Re: Funky Wavy Soffit

No. I got up on the wrong side of the bed and that's a face plant into a a 
rough cedar wall. still pulling out splinters, Brian. But do you get my point? 
You may be looking at the reference numbers in the 2007 edition where you are 
and I'm looking at 2013 and the numbers don't match. I always tell my people to 
make it easy for customers to give you their money and that advice applies 
here. When you're asking for free help and looking for code references to argue 
a point make it easy for the other Forumites to help you. I now when I pull out 
the book to help and 8.6.5.3 is not the 48" rule because you're using a 
different edition than I am, then I'm done looking, but tell me the edition you 
are using and I can pull out almost anything back to '68 (I'm missing a 
couple). I think Leyton can tell you I was able to get him a reference to a 
building built in maybe '74 that hadn't changed use and saved his client a pile 
of dough that someone who the Wizard had just bestowed a golden badge upon 
wanted spent.

On Thu, Jan 12, 2017 at 7:44 AM, Brian Harris 
<[email protected]<mailto:[email protected]>> wrote:
Ron-
You want my address?

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com<http://bvssystemsinc.com/>

From: Sprinklerforum 
[mailto:[email protected]<mailto:[email protected]>]
 On Behalf Of rongreenman .
Sent: Thursday, January 12, 2017 10:43 AM
To: 
[email protected]<mailto:[email protected]>
Subject: Re: Funky Wavy Soffit

I think that whenever someone posts a reference number and doesn't include the 
text or at least the edition he should be severely beaten.

On Thu, Jan 12, 2017 at 6:24 AM, Brian Harris 
<[email protected]<mailto:[email protected]>> wrote:
We have a grocery store that has a wavy kinda soffit (see dropbox file link 
below) around the perimeter of most of the store. The top of this soffit is 
approximately 5’0” below the overhead sprinklers & is less than 48” at the 
widest points. With that being said are additional heads needed in this lower 
soffit? In my opinion 8.6.5.2 would not apply since the pattern development is 
not affected so the next stop would be 8.6.5.3. The only thing that stands out 
to me there would be the 48” width we I do not have. So I say no additional 
heads needed below, what say you?

https://www.dropbox.com/s/3klcgh37fhowmp8/Wavy%20Soffit.pdf?dl=0

Brian Harris, CET
BVS Systems Inc.
Design Manager
bvssystemsinc.com<http://bvssystemsinc.com/>
Phone: 704.896.9989<tel:(704)%20896-9989>
Fax: 704.896.1935<tel:(704)%20896-1935>


_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



--
Ron Greenman

[email protected]<mailto:[email protected]>

253.576.9700<tel:(253)%20576-9700>

The Universe is monstrously indifferent to the presence of man. -Werner Herzog, 
screenwriter, film director, author, actor and opera director (1942-)

_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



--
Ron Greenman

[email protected]<mailto:[email protected]>

253.576.9700

The Universe is monstrously indifferent to the presence of man. -Werner Herzog, 