Let it all hang out Roland!
I hear your frustration and I think it is a result of trying to do too much
with one book.

And what is this "...installation TC"..., ?.?.?.-- when did the title of 13
change from ~installation of sprinkler systems~ to ~design and installation
of sprinkler systems~?

Brad
.
On Jan 12, 2017 11:38 AM, "Roland Huggins" <[email protected]>
wrote:

> I find it amusing that the guidance for the wall mounted soffit for which
> the top of it is LOCATED MORE THAN 18 INCHES BELOW THE DEFLECTOR is in the
> section that addresses obstruction close to the ceiling (aka the top is
> above the deflector).  This should be in 8.6.5.3.  Maybe its meant to
> balance 8.6.5.3.2 criteria for obstructions greater 48 inches that are less
> than 18 inches below the deflector.
>
> Yea my frustration is getting to me since I’ve tried multiple times to get
> the Installation TC to pay attention to where things are placed - Location
> has Meaning.  WE should see some improvement in the 2019 regarding this
> somewhat important philosophy.
>
> Roland
>
>
> Roland Huggins, PE - Senior VP Engineering
> American Fire Sprinkler Assn.
> Dallas, TX
> http://www.firesprinkler.org
>
> Fire Sprinklers Saves Lives
>
>
>
>
> On Jan 12, 2017, at 8:25 AM, Mike Stossel <[email protected]> wrote:
>
> Can you use the soffit against the wall rule from NFPA 13, 2013
> *8.6.5.1.2* *Sprinklers shall be arranged to comply with one of the
> following arrangements:
> (1) Subsection 8.5.5.2, Table 8.6.5.1.2, and Figure 8.6.5.1.2(a) shall be
> followed.
> (2) Sprinklers shall be permitted to be spaced on opposite sides of
> obstructions not exceeding 4 ft (1.2 m) in width, provided the distance
> from the centerline of the obstruction to the sprinklers does not exceed
> one-half the allowable distance permitted between sprinklers.
> (3) Obstructions located against the wall and that are not over 30 in.
> (762 mm) in width shall be permitted to be protected in accordance with
> Figure 8.6.5.1.2(b).
> (4) Obstructions located against the wall and that are not over 24 in.
> (610 mm) in width shall be permitted to be protected in accordance with
> Figure 8.6.5.1.2(c). The maximum distance between the sprinkler and the wall
> shall be measured from the sprinkler to the wall behind the obstruction
> and not to the face of the obstruction.
> *A.8.6.5.1.2 *The intent of 8.6.5.1.2(3) is to apply to soffits that are
> located within the 18 in. (457 mm) plane from the sprinkler deflector. A
> soffit or other obstruction (i.e., shelf) located against a wall that is
> located entirely below the 18 in. (457 mm) plane from the sprinkler
> deflector should be in accordance with 8.6.5.3.3. *(See Figure
> A.8.6.5.1.2.)*
>
>
> Mike Stossel *SET*
> [image: 400dpiLogoCropped]
> 36 Barren Road
> East Stroudsburg, PA 18302
> Office: 973-670-2627 <(973)%20670-2627>
> [email protected]
>
> *From:* Sprinklerforum [mailto:[email protected].
> org <[email protected]>] *On Behalf Of 
> *rongreenman
> .
> *Sent:* Thursday, January 12, 2017 11:00 AM
> *To:* [email protected]
> *Subject:* Re: Funky Wavy Soffit
>
> No. I got up on the wrong side of the bed and that's a face plant into a a
> rough cedar wall. still pulling out splinters, Brian. But do you get my
> point? You may be looking at the reference numbers in the 2007 edition
> where you are and I'm looking at 2013 and the numbers don't match. I always
> tell my people to make it easy for customers to give you their money and
> that advice applies here. When you're asking for free help and looking for
> code references to argue a point make it easy for the other Forumites to
> help you. I now when I pull out the book to help and 8.6.5.3 is not the
> 48" rule because you're using a different edition than I am, then I'm done
> looking, but tell me the edition you are using and I can pull out almost
> anything back to '68 (I'm missing a couple). I think Leyton can tell you I
> was able to get him a reference to a building built in maybe '74 that
> hadn't changed use and saved his client a pile of dough that someone who
> the Wizard had just bestowed a golden badge upon wanted spent.
>
> On Thu, Jan 12, 2017 at 7:44 AM, Brian Harris <[email protected]>
> wrote:
>
> Ron-
> You want my address?
>
> *Brian Harris, CET*
> BVS Systems Inc.
> bvssytemsinc.com <http://bvssystemsinc.com/>
>
> *From:* Sprinklerforum [mailto:[email protected].
> org] *On Behalf Of *rongreenman .
> *Sent:* Thursday, January 12, 2017 10:43 AM
> *To:* [email protected]
> *Subject:* Re: Funky Wavy Soffit
>
> I think that whenever someone posts a reference number and doesn't include
> the text or at least the edition he should be severely beaten.
>
> On Thu, Jan 12, 2017 at 6:24 AM, Brian Harris <[email protected]>
> wrote:
> We have a grocery store that has a wavy kinda soffit (see dropbox file
> link below) around the perimeter of most of the store. The top of this
> soffit is approximately 5’0” below the overhead sprinklers & is less than
> 48” at the widest points. With that being said are additional heads needed
> in this lower soffit? In my opinion 8.6.5.2 would not apply since the
> pattern development is not affected so the next stop would be 8.6.5.3. The
> only thing that stands out to me there would be the 48” width we I do not
> have. So I say no additional heads needed below, what say you?
>
> https://www.dropbox.com/s/3klcgh37fhowmp8/Wavy%20Soffit.pdf?dl=0
>
> *Brian Harris, CET*
> BVS Systems Inc.
> Design Manager
> bvssystemsinc.com
> Phone: 704.896.9989 <(704)%20896-9989>
> Fax: 704.896.1935 <(704)%20896-1935>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
>
>
> --
> Ron Greenman
>
> [email protected]
>
> 253.576.9700 <(253)%20576-9700>
>
> The Universe is monstrously indifferent to the presence of man. -Werner
> Herzog, screenwriter, film director, author, actor and opera
> director (1942-)
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
>
>
>
> --
> Ron Greenman
>
> [email protected]
>
> 253.576.9700 <(253)%20576-9700>
>
> The Universe is monstrously indifferent to the presence of man. -Werner
> Herzog, screenwriter, film director, author, actor and opera
> director (1942-)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to