where and by whom:    **Answer:  robust debate and 2016 NFPA 14
-7.10.1.3.2. **

14 is very clear:

 ** Answer:  If very clear, Then why the robust debate for many years?  If
one side of the argument were clearly superior, the other side should have
rested their case.  Playing my own devil's advocate, it is admitted that
new ideas take decades to penetrate an industry, even in this age of social
media .  It is as Max Plank said "science advances one funeral at a time
(each funeral removing another piece of intransigent old wood that up until
then -- would not bend). **

7.10.1.3.1.1 states that in combined systems the water supply for
sprinklers and an AUTOMATIC standpipe system, “… shall be based on the
sprinkler system demand (including any hose stream demand) or the standpipe
demand, whichever is greater.”

 **A:  -7.10.1.3.2, partially sprinklered building **

And such a calculation is only required of an automatic standpipe system
because a manual is calculated from the FDC and represents a completely
separate water supply from the sprinklers.

**A: How does a manual calculation from the FDC legitimize the requirement
to verify that the automatic water supply meets the standpipe demand?  It
seems to my old intransigent woody brain, given that if an automatic water
supply were proposed, one would then reasonably require a calculation to
verify this automatic water source supplied the standpipe demand -- even if
there were no manual standpipe calculation. **

And not that anyone asked, but let’s clarify that standpipes are *a
separate system *from sprinklers hydraulically *even when they’re combined*.
(underline added)

**A: I and most of your audience know what you mean, but  the above
sentence "...are *a separate system*  ... *even when they're combined*" ,
 is logical fallacy at
a simple, literal linguistic level.  It is realized the explanation is an
administrative distinction, not a distinction water flow would make during
a fire.   It is generous that the intention of the NFPA 14 and 13
committees is shared here.

Another logical instance for reflection is created if ---Standard for
Standpipes (NFPA 14) wants the designer to go to the Standard for
Sprinklers (NFPA 13) to execute this hydraulic calculation per common
practice.  If a cross-Standard reference is the intention, then why doesn't
 NFPA 14 Standpipe Standard mention in the main body of text -7.10.1.3.2
that it wants the designer to migrate to NFPA 13 Sprinkler Standard to
finish the hydraulics?   NFPA 14 -5.4.1.3 is not afraid to explicitly refer
the designer to NFPA 13 at its main body of text.  When one is designing
and using the NFPA 14 Standard for Standpipes at -7.10.1.3.2, it is a
logical (even if an unsanctioned Committee practice) assumption to conduct
the primary calculation as standpipe system (e.g. 1,250 gpm for a large
system in partially sprinklered building) and then supplement the primary
calculation with the sprinkler system demand, not the reverse.

Your argument is sympathetically heard.  But if Standard prose don't go
into woody-headed mortals such as myself without accompanying
interpretations, we are left to divine, only from the original script that
the Standard offers us there.  Why would the Standard for Standpipes not
clear up this issue and settle the debate?    Maybe because the:

a.  issue is 'very clear' and there is not much to clean up, or
b.  change doesn't come easy to Committees as well as old guys like me,
  1. it is embarrassing to make corrections to one's own writing,
especially in the safety industry
  2. there is the spectre of liability as past prescriptions might now be
opined of inferior quality.  In such case, the,Good Samaritan law should
apply. as NFPA committee work is far and away well intentioned.
c.  some committee members make salary from interpreting the very
obfuscatory script they sometimes write, or their colleagues write, or
their predecessors wrote, and
d.  NFPA makes money teaching these 'secrets' to denizens at the near and
far reaches of their empire where these standard practices have not yet
trickled down, or
e).  it is too difficult for a prescriptive Standard to write out every
conceivable instruction for every occasion, and so great-writing is good
enough.

It is argued that item "e). is wrong and that it is not too difficult to
write better than great; it is virtually impossible.  With the seemingly
unpredictable elements in our lives (at least at the quantum level ;-) we
simply can not prescriptively write Standards that will address every
situation, let alone write entire volumes without the occasional
self-conflict.  Writing safety prescriptions is hard to do.  That is why
intentions should be written too.  Intentions should be written into the
main text of the prescriptions.  But if this happened, would there be as
many transactions exchanged on the interpretations and classroom
explanations?

Taking alternative position to committee opinion is very disconcreting --
there is a tidal surge of branding one is swimming in, and potentially a
lot of bank to be losing. BIG THANKS go out to every safety committee
member and code framer that offers their time on committee and especially
whom share their opinion in public forums such as this one.  Steve
generously gives of his time and recognized superior expertise, garnered
through many months of unpaid contribution to enhancing these safety
committees.   I am indebted to him for many lessons.   Steve, Roland, Ken
and the many sisters and brethren like them whom are sharing news we can
use on these public forums; they are the exception.   Realize most
committee members do not ring in when questioned.

Scot Deal