Sounds like we need an NFPA 14 Handbook.

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of å... ....
Sent: Thursday, February 9, 2017 6:56 PM
To: [email protected]
Subject: Committee Intention and Reducing Sprinklers' Pressure in a Combined 
Standpipe/Sprinkler System


To put this in context, citations are referenced to the 2016 NFPA 14, so as to 
be more relevant to standing Committe members.


On Thu, Feb 9, 2017 at 10:07 PM, Steve Leyton 
<[email protected]<mailto:[email protected]>> wrote:
You’ve taken much of what I said out of context.


We can hope for a theoretical world in which the 'secret' or 'implied' or 
'intention' of the Committee needs to be divined, but few designers whom NFPA 
is reaching out to in the hinterlands, grew up in the culture of 'United States 
common practice'.  They design on what they have, mostly static text.

I said that even when sprinklers and standpipes are combined they are separate 
systems HYDRAULICALLY.  It is absolutely NOT required to combine the demands as 
you implied with your statement this morning, even with the qualifier of a 
partially sprinklered building.

​We agree, and we realize statement 'combined is separate' was to be applied 
adminstratively.   But there appears no clear wording in 2016 NFPA 14 
-7.10.1.3.2 to convince me that the demand of the partial sprinklered system 
should NOT be combined with standpipe demand.   If your vision as discussed 
here is truly what the NFPA 14 committee intends (and I believe your vision of 
the Committee you serve on, to be accurate ) then perhaps the Committee should 
be bold enough to write their intention in plain, simple English.



7.10.1.3.1 implies that you cannot combine the systems if the building is 
partially sprinklered (it could be worded better, to be sure).  In that case, 
you would have to determine the hydraulic demand of two completely separate 
systems.  If a building is fully sprinklered per 13 or 13R, then you select the 
more demanding of the two (separate calc’s because they are hydraulically 
designed independently of one another) and that becomes your benchmark water 
supply for sizing the COMBINED system piping that serves standpipe hose 
connections and sprinklers.

​A:  "implies"?  How is a 2nd-year designer supposed to know what NFPA 
"implies" when I am having problems reading the implication?    Maybe NFPA 14 
committee members are so close to their subject that instead of seeing the 
division created by black and white text....you are including in your 
interpretation granularity from thousands of backroom details, meetings and 
readings which the NFPA subscriber does not contain in their experience.



The NFPA 14 committee added 7.10.13.1.1 in the 2013 edition BECAUSE there has 
been long-running debate and confusion.   This change was reactive to and 
intended to be companion to the change in NFPA 13, 2010 edition that added 
A.11.1.6.6 (as it was numbered in 2010) that clarifies that it isn’t the intent 
to add standpipe demand as a hose stream to a sprinkler calculation.   So let’s 
not allow history to blur the focus both committees have brought to the issue 
of combined systems calculation; better late than never.   It
​​
IS clear in my opinion that it is not the intent of either standard to require 
concurrent demands in any form.

"Clear in your opinion"  regarding "intent", as justification for the written 
guidance on a fundamental and core procedure to the NFPA 14 standard is good.  
But not good enough for me.  You have my extreme confidence (Pb > 0.99) in the 
accuracy of your depection of the Committee's intention for sprinklered 
buildings with standpipes.  Not so for partially sprinklered buildings.

I recognize that I am arguing against the highly regarded brand of the NFPA 
institution and its well deserved reputation.  I realize that I am branded a 
non-team player for calling the question.  My intention is not to throw stones, 
my intention is to offer suggestions for improvement.  Sure, it would be better 
for NFPA if these comments were made in private.  Better for me too, probably.  
But reading this kind of stuff just might get some young designers the courage 
to challenge some of their own problems to a more meaningful solution.  
Sometimes watching and listening to a debate, teaches the listener how to 
debate and make non-personal,  goal-oriented statements.  ​More accolades, 
again,  to NFPA Standards committees.  Without NFPA, I would not have this job 
interpreting what they write.

NFPA 14 would widen the range of its clear intention with hydraulic 
calculations if we change 2016 NFPA 14 -7.10.1.3.1.1 from  "In a building 
protected in accordance with NFPA 13 or NFPA 13R, the water supply..."   to   
"in a building substantially protected with a sprinkler system in accordance to 
local building codes or risk acceptance, the water supply..."


Your theoretical regarding a partially sprinklered building and an automatic 
water supply (presumably for a standpipe system) is just that – purely 
theoretical.   There is NOTHING in the codes or referenced standards that 
requires an automatic water supply be furnished for the manual (presumably 
Class 1) elements of a low- or mid-rise building that doesn’t require an 
automatic water supply.  You state that
​​
it goes to reason that an automatic water supply (ostensibly to meet demand of 
sprinklers and/or Class II hose connections) would be calculated to meet the 
demand of a manual standpipe system but that would potentially entail upgrading 
a pump from 100 or 250 GPM to 1000 GPM, electrical system upgrades, maintenance 
issues, testing costs, etc., etc.   It does NOT go to reason that such an 
application would be a good idea; manual standpipe systems are the preferred 
means for fire departments to control their water supplies in a fire fight.  
Even in a building equipped with an automatic standpipe, engineers and incident 
commanders are trained to not trust building systems and they will override 
pumps as necessary, so long as they have the capacity to pump to the top of a 
building with their trucks.

1.  ​I prefer manual standpipes as well, but the rest of the planet is not 
entirely on board with this strategy
2.  the building is real,  not theoretical.
3.  I did not say " it goes to reason that an automatic water supply would be 
calculated to meet the demand of a manual system."  Not even close.   You 
mistook the denotative and connotaive intent of the writing.  What I wrote 
stands for itself but I will paraphrase it again for further clarity.  The 
logical point is, "we don't calculate an automatic standpipe system only 
because there is a manual sysetm calculation.  No,  we calculate the automatic 
system because it is installed."  Reread your statement, provided below:

" And such a calculation is only required of an automatic standpipe system 
because a manual is calculated from the FDC and represents a completely 
separate water supply from the sprinklers. "

Simply because a couple of logical errors were made, in no way implies that 
your opinion and knowledge of the NFPA 14 intent on hydraulic calculational 
procedure for fully sprinklered buildings is anything but spot on.   This 
message is questioning the NFPA 14 intention regarding hydraulic calculation 
procedure in partially sprinklered buildings.  I think NFPA 14 intends to add 
the sprinkler and standpipe flows.

Let us revisit point 2 mentioned just a few lines above.   The example I 
mentioned, which you opined as purely theoretical, is going to C of O.   As 
suggested in the last post, it is all but impossible to frame a prescriptive 
code to capture the almost infinite possibilities that can, and sometimes will 
materialize in the real world.   If it can be built, someone someday just 
might.   Therefore, if NFPA wants to be a better design guide and sell more 
publications, it should put more of the Committee intentions ​straight into the 
main body of text, as it has done when intending the designer to leave NFPA 14 
and refer to NFPA 13 at section -5.4.1.3.

When one reads   -7.10.1.3.2  there is very little opinion, reference to NFPA 
13, or vapor whiff of an intention that the NFPA 14 Committee wanted the 
hydraulic calcuation to separate the sprinkler demands from the standpipe 
demands.  In fact, a strict reading of the wording implies just the opposite.   
Further, in  a partially sprinklered building, Section -7.10.1.3.1.1 is largely 
not applicable, since the partially sprinklered building is not protected in 
accordance with the intention of NFPA 13 (fully sprinklered with exceptions to 
electrical rooms, etc.).

The preceeding comments are based --as much as possible-- on a literal 
interpretation of 2016 Standard 14, rather than an opinion of what others 
intended.

​
Scot Deal
Excelsior Fire & Risk Engineering
gms:  +420 722 141 478<tel:+420%20722%20141%20478>  GMT + 1


The foregoing is my opinion only and is not intended to represent the NFPA 14 
Technical Committee, nor serve as an interpretation of the standard.

Steve Leyton
Protection Design & Consulting
San Diego, CA








From: Sprinklerforum 
[mailto:[email protected]<mailto:[email protected]>]
 On Behalf Of å... ....
Sent: Thursday, February 09, 2017 12:28 PM
To: 
[email protected]<mailto:[email protected]>
Subject: Committee Intention and Reducing Sprinklers' Pressure in a Combined 
Standpipe/Sprinkler System




where and by whom:    **Answer:  robust debate and 2016 NFPA 14 -7.10.1.3.2. **

14 is very clear:

 ** Answer:  If very clear, Then why the robust debate for many years?  If one 
side of the argument were clearly superior, the other side should have rested 
their case.  Playing my own devil's advocate, it is admitted that new ideas 
take decades to penetrate an industry, even in this age of social media .  It 
is as Max Plank said "science advances one funeral at a time (each funeral 
removing another piece of intransigent old wood that up until then -- would not 
bend). **

7.10.1.3.1.1 states that in combined systems the water supply for sprinklers 
and an AUTOMATIC standpipe system, “… shall be based on the sprinkler system 
demand (including any hose stream demand) or the standpipe demand, whichever is 
greater.”

 **A:  -7.10.1.3.2, partially sprinklered building **

And such a calculation is only required of an automatic standpipe system 
because a manual is calculated from the FDC and represents a completely 
separate water supply from the sprinklers.

**A: How does a manual calculation from the FDC legitimize the requirement to 
verify that the automatic water supply meets the standpipe demand?  It seems to 
my old intransigent woody brain, given that if an automatic water supply were 
proposed, one would then reasonably require a calculation to verify this 
automatic water source supplied the standpipe demand -- even if there were no 
manual standpipe calculation. **

And not that anyone asked, but let’s clarify that standpipes are a separate 
system from sprinklers hydraulically even when they’re combined. (underline 
added)

**A: I and most of your audience know what you mean, but  the above sentence 
"...are a separate system  ... even when they're combined" ,  is logical 
fallacy at
a simple, literal linguistic level.  It is realized the explanation is an 
administrative distinction, not a distinction water flow would make during a 
fire.   It is generous that the intention of the NFPA 14 and 13 committees is 
shared here.

Another logical instance for reflection is created if ---Standard for 
Standpipes (NFPA 14) wants the designer to go to the Standard for Sprinklers 
(NFPA 13) to execute this hydraulic calculation per common practice.  If a 
cross-Standard reference is the intention, then why doesn't  NFPA 14 Standpipe 
Standard mention in the main body of text -7.10.1.3.2 that it wants the 
designer to migrate to NFPA 13 Sprinkler Standard to finish the hydraulics?   
NFPA 14 -5.4.1.3 is not afraid to explicitly refer the designer to NFPA 13 at 
its main body of text.  When one is designing and using the NFPA 14 Standard 
for Standpipes at -7.10.1.3.2, it is a logical (even if an unsanctioned 
Committee practice) assumption to conduct the primary calculation as standpipe 
system (e.g. 1,250 gpm for a large system in partially sprinklered building) 
and then supplement the primary calculation with the sprinkler system demand, 
not the reverse.

Your argument is sympathetically heard.  But if Standard prose don't go into 
woody-headed mortals such as myself without accompanying interpretations, we 
are left to divine, only from the original script that the Standard offers us 
there.  Why would the Standard for Standpipes not clear up this issue and 
settle the debate?    Maybe because the:

a.  issue is 'very clear' and there is not much to clean up, or
b.  change doesn't come easy to Committees as well as old guys like me,
  1. it is embarrassing to make corrections to one's own writing, especially in 
the safety industry
  2. there is the spectre of liability as past prescriptions might now be 
opined of inferior quality.  In such case, the,Good Samaritan law should apply. 
as NFPA committee work is far and away well intentioned.
c.  some committee members make salary from interpreting the very obfuscatory 
script they sometimes write, or their colleagues write, or their predecessors 
wrote, and
d.  NFPA makes money teaching these 'secrets' to denizens at the near and far 
reaches of their empire where these standard practices have not yet trickled 
down, or
e).  it is too difficult for a prescriptive Standard to write out every 
conceivable instruction for every occasion, and so great-writing is good enough.

It is argued that item "e). is wrong and that it is not too difficult to write 
better than great; it is virtually impossible.  With the seemingly 
unpredictable elements in our lives (at least at the quantum level ;-) we 
simply can not prescriptively write Standards that will address every 
situation, let alone write entire volumes without the occasional self-conflict. 
 Writing safety prescriptions is hard to do.  That is why intentions should be 
written too.  Intentions should be written into the main text of the 
prescriptions.  But if this happened, would there be as many transactions 
exchanged on the interpretations and classroom explanations?

Taking alternative position to committee opinion is very disconcreting -- there 
is a tidal surge of branding one is swimming in, and potentially a lot of bank 
to be losing. BIG THANKS go out to every safety committee member and code 
framer that offers their time on committee and especially whom share their 
opinion in public forums such as this one.  Steve generously gives of his time 
and recognized superior expertise, garnered through many months of unpaid 
contribution to enhancing these safety committees.   I am indebted to him for 
many lessons.   Steve, Roland, Ken and the many sisters and brethren like them 
whom are sharing news we can use on these public forums; they are the 
exception.   Realize most committee members do not ring in when questioned.

​​
Scot Deal
Excelsior Fire & Risk Engineering
gms:  +420 722 141 478<tel:+420%20722%20141%20478>  GMT + 1