You’ve taken much of what I said out of context.   I said that even when 
sprinklers and standpipes are combined they are separate systems HYDRAULICALLY. 
 It is absolutely NOT required to combine the demands as you implied with your 
statement this morning, even with the qualifier of a partially sprinklered 
building.   7.10.1.3.1 implies that you cannot combine the systems if the 
building is partially sprinklered (it could be worded better, to be sure).  In 
that case, you would have to determine the hydraulic demand of two completely 
separate systems.  If a building is fully sprinklered per 13 or 13R, then you 
select the more demanding of the two (separate calc’s because they are 
hydraulically designed independently of one another) and that becomes your 
benchmark water supply for sizing the COMBINED system piping that serves 
standpipe hose connections and sprinklers.

The NFPA 14 committee added 7.10.13.1.1 in the 2013 edition BECAUSE there has 
been long-running debate and confusion.   This change was reactive to and 
intended to be companion to the change in NFPA 13, 2010 edition that added 
A.11.1.6.6 (as it was numbered in 2010) that clarifies that it isn’t the intent 
to add standpipe demand as a hose stream to a sprinkler calculation.   So let’s 
not allow history to blur the focus both committees have brought to the issue 
of combined systems calculation; better late than never.   It IS clear in my 
opinion that it is not the intent of either standard to require concurrent 
demands in any form.

Your theoretical regarding a partially sprinklered building and an automatic 
water supply (presumably for a standpipe system) is just that – purely 
theoretical.   There is NOTHING in the codes or referenced standards that 
requires an automatic water supply be furnished for the manual (presumably 
Class 1) elements of a low- or mid-rise building that doesn’t require an 
automatic water supply.  You state that it goes to reason that an automatic 
water supply (ostensibly to meet demand of sprinklers and/or Class II hose 
connections) would be calculated to meet the demand of a manual standpipe 
system but that would potentially entail upgrading a pump from 100 or 250 GPM 
to 1000 GPM, electrical system upgrades, maintenance issues, testing costs, 
etc., etc.   It does NOT go to reason that such an application would be a good 
idea; manual standpipe systems are the preferred means for fire departments to 
control their water supplies in a fire fight.  Even in a building equipped with 
an automatic standpipe, engineers and incident commanders are trained to not 
trust building systems and they will override pumps as necessary, so long as 
they have the capacity to pump to the top of a building with their trucks.


The foregoing is my opinion only and is not intended to represent the NFPA 14 
Technical Committee, nor serve as an interpretation of the standard.

Steve Leyton
Protection Design & Consulting
San Diego, CA








From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of å... ....
Sent: Thursday, February 09, 2017 12:28 PM
To: [email protected]
Subject: Committee Intention and Reducing Sprinklers' Pressure in a Combined 
Standpipe/Sprinkler System




where and by whom:    **Answer:  robust debate and 2016 NFPA 14 -7.10.1.3.2. **

14 is very clear:

 ** Answer:  If very clear, Then why the robust debate for many years?  If one 
side of the argument were clearly superior, the other side should have rested 
their case.  Playing my own devil's advocate, it is admitted that new ideas 
take decades to penetrate an industry, even in this age of social media .  It 
is as Max Plank said "science advances one funeral at a time (each funeral 
removing another piece of intransigent old wood that up until then -- would not 
bend). **

7.10.1.3.1.1 states that in combined systems the water supply for sprinklers 
and an AUTOMATIC standpipe system, “… shall be based on the sprinkler system 
demand (including any hose stream demand) or the standpipe demand, whichever is 
greater.”

 **A:  -7.10.1.3.2, partially sprinklered building **

And such a calculation is only required of an automatic standpipe system 
because a manual is calculated from the FDC and represents a completely 
separate water supply from the sprinklers.

**A: How does a manual calculation from the FDC legitimize the requirement to 
verify that the automatic water supply meets the standpipe demand?  It seems to 
my old intransigent woody brain, given that if an automatic water supply were 
proposed, one would then reasonably require a calculation to verify this 
automatic water source supplied the standpipe demand -- even if there were no 
manual standpipe calculation. **

And not that anyone asked, but let’s clarify that standpipes are a separate 
system from sprinklers hydraulically even when they’re combined. (underline 
added)

**A: I and most of your audience know what you mean, but  the above sentence 
"...are a separate system  ... even when they're combined" ,  is logical 
fallacy at
a simple, literal linguistic level.  It is realized the explanation is an 
administrative distinction, not a distinction water flow would make during a 
fire.   It is generous that the intention of the NFPA 14 and 13 committees is 
shared here.

Another logical instance for reflection is created if ---Standard for 
Standpipes (NFPA 14) wants the designer to go to the Standard for Sprinklers 
(NFPA 13) to execute this hydraulic calculation per common practice.  If a 
cross-Standard reference is the intention, then why doesn't  NFPA 14 Standpipe 
Standard mention in the main body of text -7.10.1.3.2 that it wants the 
designer to migrate to NFPA 13 Sprinkler Standard to finish the hydraulics?   
NFPA 14 -5.4.1.3 is not afraid to explicitly refer the designer to NFPA 13 at 
its main body of text.  When one is designing and using the NFPA 14 Standard 
for Standpipes at -7.10.1.3.2, it is a logical (even if an unsanctioned 
Committee practice) assumption to conduct the primary calculation as standpipe 
system (e.g. 1,250 gpm for a large system in partially sprinklered building) 
and then supplement the primary calculation with the sprinkler system demand, 
not the reverse.

Your argument is sympathetically heard.  But if Standard prose don't go into 
woody-headed mortals such as myself without accompanying interpretations, we 
are left to divine, only from the original script that the Standard offers us 
there.  Why would the Standard for Standpipes not clear up this issue and 
settle the debate?    Maybe because the:

a.  issue is 'very clear' and there is not much to clean up, or
b.  change doesn't come easy to Committees as well as old guys like me,
  1. it is embarrassing to make corrections to one's own writing, especially in 
the safety industry
  2. there is the spectre of liability as past prescriptions might now be 
opined of inferior quality.  In such case, the,Good Samaritan law should apply. 
as NFPA committee work is far and away well intentioned.
c.  some committee members make salary from interpreting the very obfuscatory 
script they sometimes write, or their colleagues write, or their predecessors 
wrote, and
d.  NFPA makes money teaching these 'secrets' to denizens at the near and far 
reaches of their empire where these standard practices have not yet trickled 
down, or
e).  it is too difficult for a prescriptive Standard to write out every 
conceivable instruction for every occasion, and so great-writing is good enough.

It is argued that item "e). is wrong and that it is not too difficult to write 
better than great; it is virtually impossible.  With the seemingly 
unpredictable elements in our lives (at least at the quantum level ;-) we 
simply can not prescriptively write Standards that will address every 
situation, let alone write entire volumes without the occasional self-conflict. 
 Writing safety prescriptions is hard to do.  That is why intentions should be 
written too.  Intentions should be written into the main text of the 
prescriptions.  But if this happened, would there be as many transactions 
exchanged on the interpretations and classroom explanations?

Taking alternative position to committee opinion is very disconcreting -- there 
is a tidal surge of branding one is swimming in, and potentially a lot of bank 
to be losing. BIG THANKS go out to every safety committee member and code 
framer that offers their time on committee and especially whom share their 
opinion in public forums such as this one.  Steve generously gives of his time 
and recognized superior expertise, garnered through many months of unpaid 
contribution to enhancing these safety committees.   I am indebted to him for 
many lessons.   Steve, Roland, Ken and the many sisters and brethren like them 
whom are sharing news we can use on these public forums; they are the 
exception.   Realize most committee members do not ring in when questioned.

Scot Deal