Sidestep the issue. If you can, pull a slight vacuum on the standpipe instead 
of pressurizing it. 


> On Feb 28, 2017, at 7:17 AM, Mike Stossel <[email protected]> wrote:
> 
> I am trying to calculate the time it will take for a 2-1/2” hose valve to 
> relieve a standpipe system of air.  I am designing a temporary standpipe 
> system in NYC and the requirement is to fill the entire system with air and a 
> single 2-1/2” hose valve needs to relieve the pressure within 3 minutes or a 
> second will need to be added.  My total system volume will be 1902 gallons 
> and the staring air pressure will be at 18psi.  Does anyone know of a way to 
> calculate this?
>  
> Thanks for the help.
>  
> Mike Stossel SET
> <image003.png>