Sounds like an automatic dry standpipe off a low differential dry valve but 
you’re not concerned about water delivery time or even water pushing out the 
air?  Just a 2 ½” outlet at the top?

Where’s Brad?

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Mike Stossel
Sent: Wednesday, March 01, 2017 9:01 AM
To: [email protected]
Subject: RE: Air Relief Time

 

The standing air pressure is a minimum of 13psi and a maximum of 18psi.  The 
gauge located at the FDC must read zero within 3 minutes of full open.  
Compressor is connected and running.  Four 4” stacks top of stack is 70’0”.

 

Thanks,

 

Mike Stossel SET



36 Barren Road

East Stroudsburg, PA 18302

Office: 973-670-2627

[email protected] <mailto:[email protected]> 

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Tom Duross
Sent: Wednesday, March 1, 2017 7:54 AM
To: [email protected] 
<mailto:[email protected]> 
Subject: RE: Air Relief Time

 

NYC has a requirement for construction standpipes in all high-rises to be 
pressurized and monitored with a placard indicating required FDC pressures for 
required flows at each floor.  Boston adopted this last year.  Roadway 
standpipes are required to be timed for water delivery but are empty and have 
automatic air vents  at the FDV’s.  What’s the application requiring exhaust of 
standing air pressure?  Is there a compressor connected and running?  
Horizontal or vertical installation?  

TD

 

Sidestep the issue. If you can, pull a slight vacuum on the standpipe instead 
of pressurizing it. 

 

 

On Feb 28, 2017, at 7:17 AM, Mike Stossel <[email protected] 
<mailto:[email protected]> > wrote:

 

I am trying to calculate the time it will take for a 2-1/2” hose valve to 
relieve a standpipe system of air.  I am designing a temporary standpipe system 
in NYC and the requirement is to fill the entire system with air and a single 
2-1/2” hose valve needs to relieve the pressure within 3 minutes or a second 
will need to be added.  My total system volume will be 1902 gallons and the 
staring air pressure will be at 18psi.  Does anyone know of a way to calculate 
this?

 

Thanks for the help.

 