I'd make sure that an air make up device is used, with the typical maintenance 
bypass.

Bruce 

> On Mar 1, 2017, at 06:18, Mike Stossel <[email protected]> wrote:
> 
> Brad is actually trying to help me off forum.  It is definitely a difficult 
> calculation to run and way beyond me.  At least if it had a dry valve I could 
> run an FDT calculation, but it has nothing.  It is a closed system with an 
> air compressor only.  A 2 ½” dump valve is located at each FDC with a gauge.  
> When the fire department arrives they open the dump valve and when it hits 
> zero starts pressurizing the temporary standpipe.  The air in the system is 
> just supervisory.  You have low pressure and high pressure alarms attached 
> just like a dry valve, but minus the dry valve.  The air is just to make sure 
> the system is always solid for the fire department.  If someone should tamper 
> with it or break something the alarm will notify that a repair is needed. 
>  
> Mike Stossel SET
> <image001.png>
> 36 Barren Road
> East Stroudsburg, PA 18302
> Office: 973-670-2627
> [email protected]
>  
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of Tom Duross
> Sent: Wednesday, March 1, 2017 9:07 AM
> To: [email protected]
> Subject: RE: Air Relief Time
>  
> Sounds like an automatic dry standpipe off a low differential dry valve but 
> you’re not concerned about water delivery time or even water pushing out the 
> air?  Just a 2 ½” outlet at the top?
> Where’s Brad?
>  
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of Mike Stossel
> Sent: Wednesday, March 01, 2017 9:01 AM
> To: [email protected]
> Subject: RE: Air Relief Time
>  
> The standing air pressure is a minimum of 13psi and a maximum of 18psi.  The 
> gauge located at the FDC must read zero within 3 minutes of full open.  
> Compressor is connected and running.  Four 4” stacks top of stack is 70’0”.
>  
> Thanks,
>  
> Mike Stossel SET
> <image004.png>
> 36 Barren Road
> East Stroudsburg, PA 18302
> Office: 973-670-2627
> [email protected]
>  
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of Tom Duross
> Sent: Wednesday, March 1, 2017 7:54 AM
> To: [email protected]
> Subject: RE: Air Relief Time
>  
> NYC has a requirement for construction standpipes in all high-rises to be 
> pressurized and monitored with a placard indicating required FDC pressures 
> for required flows at each floor.  Boston adopted this last year.  Roadway 
> standpipes are required to be timed for water delivery but are empty and have 
> automatic air vents  at the FDV’s.  What’s the application requiring exhaust 
> of standing air pressure?  Is there a compressor connected and running?  
> Horizontal or vertical installation? 
> TD
>  
> Sidestep the issue. If you can, pull a slight vacuum on the standpipe instead 
> of pressurizing it. 
>  
>  
> On Feb 28, 2017, at 7:17 AM, Mike Stossel <[email protected]> wrote:
>  
> I am trying to calculate the time it will take for a 2-1/2” hose valve to 
> relieve a standpipe system of air.  I am designing a temporary standpipe 
> system in NYC and the requirement is to fill the entire system with air and a 
> single 2-1/2” hose valve needs to relieve the pressure within 3 minutes or a 
> second will need to be added.  My total system volume will be 1902 gallons 
> and the staring air pressure will be at 18psi.  Does anyone know of a way to 
> calculate this?
>  
> Thanks for the help.
>  
> Mike Stossel SET
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to