NFPA 13 (10) section 11.3.1.1 also includes “adjacent”.  What does this
mean actually?  4 heads on the same line regardless of the walls or 4 heads
in the same area but may be supplied from different lines?  The pictures in
the appendix are not very clear.

Thanks,

Dewayne



*From:* Sprinklerforum [mailto:
[email protected]] *On Behalf Of *
[email protected]
*Sent:* Friday, July 08, 2016 9:13 AM
*To:* sprinklerforum
*Subject:* Re: Dwelling Unit Sprinkler Calc



In response to the original question, is it just me or are we over-thinking
this?

NFPA 13 says that when using residential heads, you calculate the 4 heads
that produce the greatest hydraulic demand.  No mention of units, rated
walls, corridors, type of construction, etc.



I didn't know George Church, but I would have liked him.


------------------------------

*From: *"Travis Mack" <[email protected]>
*To: *[email protected], "sprinklerforum" <
[email protected]>
*Sent: *Tuesday, July 5, 2016 3:44:35 PM
*Subject: *Re: Dwelling Unit Sprinkler Calc



I'd probably grab the adjacent sprinkler in the adjacent room.







Travis Mack, SET

MFP Design, LLC

"Follow" us on Facebook:
https://www.facebook.com/pages/MFP-Design-LLC/92218417692

Send large files to MFP Design via:

https://www.hightail.com/u/MFPDesign



Sent from my iPhone


On Jul 5, 2016, at 12:34 PM, Bob <[email protected]> wrote:



I have a NFPA 13 building with Dwelling Units.  They each have three
Residential Sprinklers.  13 requires a four head calc.  Can I calc the 3
residential sprinklers and pick up one QR sprinkler in the corridor and
still satisfy the 4 head requirement?  Or, should I pick up one residential
sprinkler from an adjacent dwelling room?



Thank you,



Bob Knight, CET III

208-318-3057

<image002.jpg>



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to