NFPA 13 (10) section 11.3.1.1 also includes “adjacent”. What does this mean actually? 4 heads on the same line regardless of the walls or 4 heads in the same area but may be supplied from different lines? The pictures in the appendix are not very clear.
Thanks, Dewayne *From:* Sprinklerforum [mailto: [email protected]] *On Behalf Of * [email protected] *Sent:* Friday, July 08, 2016 9:13 AM *To:* sprinklerforum *Subject:* Re: Dwelling Unit Sprinkler Calc In response to the original question, is it just me or are we over-thinking this? NFPA 13 says that when using residential heads, you calculate the 4 heads that produce the greatest hydraulic demand. No mention of units, rated walls, corridors, type of construction, etc. I didn't know George Church, but I would have liked him. ------------------------------ *From: *"Travis Mack" <[email protected]> *To: *[email protected], "sprinklerforum" < [email protected]> *Sent: *Tuesday, July 5, 2016 3:44:35 PM *Subject: *Re: Dwelling Unit Sprinkler Calc I'd probably grab the adjacent sprinkler in the adjacent room. Travis Mack, SET MFP Design, LLC "Follow" us on Facebook: https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Send large files to MFP Design via: https://www.hightail.com/u/MFPDesign Sent from my iPhone On Jul 5, 2016, at 12:34 PM, Bob <[email protected]> wrote: I have a NFPA 13 building with Dwelling Units. They each have three Residential Sprinklers. 13 requires a four head calc. Can I calc the 3 residential sprinklers and pick up one QR sprinkler in the corridor and still satisfy the 4 head requirement? Or, should I pick up one residential sprinkler from an adjacent dwelling room? Thank you, Bob Knight, CET III 208-318-3057 <image002.jpg> _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org