And with the 3000 sq ft you can go to 0.07 density and likely use small orifice 
sprinklers to cut down on over discharge. 

Travis Mack, SET
MFP Design, LLC
"Follow" us on Facebook: 
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone

> On Mar 1, 2017, at 10:08 AM, Steve Leyton <[email protected]> wrote:
> 
> Even though it’s not the specific topic of this thread, I feel compelled to 
> add that, where certain unsprinklered combustible concealed spaces are 
> present, the triggers for 8-sprinkler and 3,000 sq. ft. design areas have 
> tightened in the past two editions of the standard,.  You use the same 
> methodology, i.e. walls are transparent, you pick up sprinklers in the 
> communicating spaces the same way, etc., but the design area essentially 
> doubles.
>  
> Steve L.
>  
>  
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of Travis Mack
> Sent: Wednesday, March 01, 2017 8:51 AM
> To: [email protected]
> Subject: Re: Dwelling Unit Sprinkler Calc
>  
> You can use small room rule and do room area divided by number of heads to 
> get 0.1 flow. Then compare that to data sheet. 
> 
> Travis Mack, SET
> MFP Design, LLC
> "Follow" us on Facebook: 
> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
> Send large files to MFP Design via:
> https://www.hightail.com/u/MFPDesign
>  
> Sent from my iPhone
> 
> On Mar 1, 2017, at 9:43 AM, Ed Kramer <[email protected]> wrote:
> 
> I agree – 4 heads regardless of walls, even if the walls are rated.  It 
> creates a bit of a penalty when using residential sprinks.  I understand the 
> reasoning back when we didn’t provide a .10 density, but not so much now.   
> Sometimes I’ve found it’s more economical to switch to QR sprinks and then 
> utilize the room design method.  Just depends on the particulars of your 
> layout.
>  
> Ed Kramer
> Bamford Fire
>  
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of Travis Mack
> Sent: Wednesday, March 01, 2017 10:17 AM
> To: [email protected]
> Subject: Re: Dwelling Unit Sprinkler Calc
>  
> It is regardless of walls. I pick 4 on one line if they are the most 
> demanding. If unsure, just throw on a few calc areas and take the most 
> demanding one. (Another plug for Autosprink - draw the extra remote areas. 
> Tell it to keep most demanding and you are done). 
> 
> Travis Mack, SET
> MFP Design, LLC
> "Follow" us on Facebook: 
> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
> Send large files to MFP Design via:
> https://www.hightail.com/u/MFPDesign
>  
> Sent from my iPhone
> 
> On Mar 1, 2017, at 9:05 AM, Dewayne Martinez <[email protected]> 
> wrote:
> 
> NFPA 13 (10) section 11.3.1.1 also includes “adjacent”.  What does this mean 
> actually?  4 heads on the same line regardless of the walls or 4 heads in the 
> same area but may be supplied from different lines?  The pictures in the 
> appendix are not very clear.
> Thanks,
> Dewayne
>  
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of [email protected]
> Sent: Friday, July 08, 2016 9:13 AM
> To: sprinklerforum
> Subject: Re: Dwelling Unit Sprinkler Calc
>  
> In response to the original question, is it just me or are we over-thinking 
> this?
> NFPA 13 says that when using residential heads, you calculate the 4 heads 
> that produce the greatest hydraulic demand.  No mention of units, rated 
> walls, corridors, type of construction, etc.
>  
> I didn't know George Church, but I would have liked him.
>  
> From: "Travis Mack" <[email protected]>
> To: [email protected], "sprinklerforum" 
> <[email protected]>
> Sent: Tuesday, July 5, 2016 3:44:35 PM
> Subject: Re: Dwelling Unit Sprinkler Calc
>  
> I'd probably grab the adjacent sprinkler in the adjacent room. 
>  
>  
>  
> Travis Mack, SET
> MFP Design, LLC
> "Follow" us on Facebook: 
> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
> Send large files to MFP Design via:
> https://www.hightail.com/u/MFPDesign
>  
> Sent from my iPhone
> 
> On Jul 5, 2016, at 12:34 PM, Bob <[email protected]> wrote:
>  
> I have a NFPA 13 building with Dwelling Units.  They each have three 
> Residential Sprinklers.  13 requires a four head calc.  Can I calc the 3 
> residential sprinklers and pick up one QR sprinkler in the corridor and still 
> satisfy the 4 head requirement?  Or, should I pick up one residential 
> sprinkler from an adjacent dwelling room?
>  
> Thank you,
>  
> Bob Knight, CET III
> 208-318-3057
> <image002.jpg>
>  
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>  
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________