“Maybe”?

I have come across instances where the code choices made by the architect 
caused a need for sprinklers in a situation similar to this. Your best bet will 
be to have the Engineer walk you through the code path that led them to 
sprinklers. I have been surprised by roundabout exceptions/counter-exceptions 
more than once. Or maybe they have made an error. If you want them to believe 
you – you will likely have to do the same exercise.

Matt

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of David Autry
Sent: Friday, March 03, 2017 9:37 AM
To: [email protected]
Subject: Canopy

I’ve got a 4 story Hotel with a detached Canopy.
V-A Construction type protected NFPA 13 (2013), R-1 occupancy.
The Canopy is of non-combustible construction and detached from the building. I 
have an Engineer telling me I need to protect this structure. Am I missing 
something?
2006 IBC, Building code.

Thanks,

David Autry