Is it a canopy or porte-cochere where vehicles enter or leave? IBC CANOPY 
definition: A structure, enclosure or shelter constructed of fabric or pliable 
materials supported by any manner, except by air or the contents it protects, 
and is open without sidewalls or drops on 75 percent or more of the perimeter.

 

AHJ’s often require porte-cochere's to be sprinklered (even if detached) due to 
the higher hazard of fueled vehicles. Many jurisdictions amend their codes to 
limit the size of canopies that don't require sprinkler protection, as well.

 

Travis E. Allen, PE

Principal

 

Allen Engineering, PLLC

 

From: David Autry [mailto:[email protected]] 
Sent: Friday, March 3, 2017 7:37 AM
To: [email protected]
Subject: Canopy

 

I’ve got a 4 story Hotel with a detached Canopy.

V-A Construction type protected NFPA 13 (2013), R-1 occupancy.

The Canopy is of non-combustible construction and detached from the building. I 
have an Engineer telling me I need to protect this structure. Am I missing 
something?

2006 IBC, Building code.

 

Thanks,

 

David Autry

 

Meininger Fire Protection

2521 West L Street, Suite 5

Lincoln, NE 68522

402.466.2616

402.466.2617 fax

[email protected]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to